Hi All;
I have a flat with 6 areas warmed via underfloor heating. Each of the areas are controlled by its own thermostat Microline Ultra-Thin Thermostat with display, and there are 2 models used:
2 x OTN2-1991 with floor sensor (bathroom)
4 x OTN2-1999 with built-in room sensor (other rooms)
Microline Manual Link:
Power is applied on Microline terminals 1 and 2, via the setup explained below.
These 6 individual areas are combined into 3 major areas. These major areas are controlled via its own contactor HAGER ES 200 (25A/230V) controlled by a Drayton Timer.
Because of the "clank" noise when contactors are switched-on/off and the humming noise when on, I decided to replace this mechanical system with a Solid State Contactor (Croydon CRKA2430).
Great!! the clank and humming noise are gone!! However due to the way the Solid State Contactor operates, I noticed that there is a voltage leakage of about 16VAC, enough to mess-up the programming on the Microline Thermostat.
Not sure how to resolve the voltage leak, but my question is: Do you know of any 25A Ultra Quiet contactor, that will not make a huge clank and humming noise pls?
Many thanks
Lucio
View attachment 35468
View attachment 35469
View attachment 35470
View attachment 35471
View attachment 35472
I have a flat with 6 areas warmed via underfloor heating. Each of the areas are controlled by its own thermostat Microline Ultra-Thin Thermostat with display, and there are 2 models used:
2 x OTN2-1991 with floor sensor (bathroom)
4 x OTN2-1999 with built-in room sensor (other rooms)
Microline Manual Link:
Power is applied on Microline terminals 1 and 2, via the setup explained below.
These 6 individual areas are combined into 3 major areas. These major areas are controlled via its own contactor HAGER ES 200 (25A/230V) controlled by a Drayton Timer.
Because of the "clank" noise when contactors are switched-on/off and the humming noise when on, I decided to replace this mechanical system with a Solid State Contactor (Croydon CRKA2430).
Great!! the clank and humming noise are gone!! However due to the way the Solid State Contactor operates, I noticed that there is a voltage leakage of about 16VAC, enough to mess-up the programming on the Microline Thermostat.
Not sure how to resolve the voltage leak, but my question is: Do you know of any 25A Ultra Quiet contactor, that will not make a huge clank and humming noise pls?
Many thanks
Lucio