Discuss Ring continuity voltage at dead test in the UK Electrical Forum area at ElectriciansForums.net

N

newtrade

Hi guys

doing a ring continuity test . R1,Rn,R2 values all okay. Done figure of 8. Tested at each point and not allowing continuity test due to 8 volts. Stuck on what this is? Any ideas ?
 
Do a walk around and visually check that everything is off, I have been into houses before and someone has Henley blocked before the meter to another CU.
Other option is they borrowed a supply from next door.

Saying that I was at a house last week, CU change - up in the attic was 2 rings. One for the house I was working on and 1 for next door.

It turned out the attic wall as 2ft over next door instead of directly over the separating wall
 
Hi guys

doing a ring continuity test . R1,Rn,R2 values all okay. Done figure of 8. Tested at each point and not allowing continuity test due to 8 volts. Stuck on what this is? Any ideas ?

r1 r2 and rn you mean I hope
 

Reply to Ring continuity voltage at dead test in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi guys. Having a weird problem in a house that has suddenly happened. One half of the ring main has 240ish volts (fluctuates of course), and...
Replies
9
Views
467
Extremely low voltage on 120v line Hi, I’m not an electrician but my home has 20 amp breaker that has only one outdoor outlet on it with a GFCI...
Replies
2
Views
540
Hey there, Sorry I’ve just joined up. I’m a qualified electrician/Electrical engineer. Recently sat my 2391-52. My question is I had a fault...
Replies
4
Views
1K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi All, I've installed a Lorex doorbell recently, but it is not turning on. I did some tests using a multimeter and this is what I found...
Replies
5
Views
983

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock