You've got it... If it had been glanded straight into the metalclad sockets and used piranha nuts it would of been better.
When you look at this type of system in the cold light of day regarding the earthing/cpc and ignore the L and N conductors the and the Armour being suitable for use as a cpc, then there isn't much difference from that to a metal conduit install. You don't run a cpc in metallic conduit you fly lead from the earth stud in the box to the earth terminal on the socket face plate, no difference in doing the same with the SWA install is there?
 
If this was a standard 4mm radial without the addition of an extra help for the live and neutral (in the form of another 2 cores to assist) maybe the collective eyebrows would not be so lifted :)
 
If this was a standard 4mm radial without the addition of an extra help for the live and neutral (in the form of another 2 cores to assist) maybe the collective eyebrows would not be so lifted :)
Wash your mouth out it is a 13A socket and MUST be a ring final;)
 
Never uses two core swa for sockets, but when i use metal clad socket ( am waiting to hear "why") but i alway take the paint off in the inside round the knockout (it reassure me)
 
Never uses two core swa for sockets, but when i use metal clad socket ( am waiting to hear "why") but i alway take the paint off in the inside round the knockout (it reassure me)
Should be done on ALL metal enclosures, where conduit or SWA installations, lost count of the number of hours I spent filing coupler ends flat, filing lock nuts, cleaning paint from enclosures, not for reassurance, but for a good contact, a lost practice these days I'm afraid.
 
When I started out I was told to thread the conduit and use two lock nuts tightened up on to themselves and a female bush on the inside, must admit not done that for years.
 
When I started out I was told to thread the conduit and use two lock nuts tightened up on to themselves and a female bush on the inside, must admit not done that for years.
All sorts of ways of doing things back in the good old days Westy
 

Reply to Ring Final Circuit wired in 4 core SWA in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Carrying out an EICR and came across a ring final circuit wired to the first of six metal clad sockets in 2.5mm 5 core SWA. Obviously 2 cores for...
Replies
5
Views
920
Morning all So the site I'm based at recently had some work done (think partitioners). This package of work included electrical. This was...
Replies
44
Views
8K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
Have come accross a job where house ring run in T/E but has an old extension with earthed metal conduit used for sockets and only live and neutral...
Replies
6
Views
1K
I have a metal Hager sub CU, 10 way RCBO, installed in 2018 in an accessible attic space, this sub-CU being fed from another unit close to the...
Replies
11
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock