I'm doing a PIR on my flat and I've come across a fault I can't work out.

I'm getting a very low (about 0.1Meg Ohm) insulation resistance between Neutral and Line conductors on one of the ring circuits. However I'm not getting continuity between Line and Neutral and the MCB isn't tripping.

The symptoms would suggest there's a load on the circuit somewhere but I've unplugged everything attached to the ring and disconnected the neon in the fused spur to the washing machine.

I was getting continuity (230 Ohms) together with a low insulation resistance until I located a bell transformer spurred from the ring.

When I detached the transformer the continuity disappeared and I thought I'd cracked it......but the low IR remained.

The ring is wired in singles in steel conduit.

Does anyone have any ideas on my current situation

Any thoughts wold be appreciated.

Al
 
Hi wirepuller + phil,

Just as I posted I had a brain wave (or doh ! moment). There's a small storage cupboard outside my front door.. just opened it up and there's an unused thermostat on the wall.
I'll pull all the rubbish out and give it a test tomorrow.

Ta

Al
 
Last edited:
grrrrrrrr singles ! Reading borough councils fav ! was on a 36 rewire project last year with them ! Good luck as said boiler etc we get nice things spurred off all sorts in our game ! split ring and test both legs then split faulty leg etc
 
Thanks kung,

Started splitting the ring up but like you said..the joys of single.. it's not easy to guess what point is next in the ring.

..bit of a mind bender..

fingers crossed for the redundant thermostat : )
 
Well Gentlemen...

The thermostat wasn't the problem. It was attached to exactly nothing !

BUT.. during some spring cleaning this morning my wife drew my attention to a hollow sound as the hoover hit the wall behind some storage boxes.

It looks like there's an old fireplace behind the panel which I hope is the cause of the problem.

They did such a good job of paneling it in you really have to squint to see the join ...

Club hammer and bolster time on Wednesday :)

Al
 
Last edited:
Soo....

At the risk of looking like a complete idiot, I've decided to post my findings.

When I got the time I took a hammer to the sealed fire place and successfully made a complete mess of the wall.

And behind the plaster board was ..wait for it.....

absolutely bugger all !

My only option was to split the ring in stages and hope to identify the problem.

And....

my first IR test at the board showed NO FAULT.

I'd found this fault twice having taken out all appliances and loads on two separate occasions !

The head scratcher for me is the fact that mis-test on a IR test would give a satisfactory (High M ohm) result. My result suggested I was actually testing the circuit and finding something dodgy.

Or maybe I didn't truly take the bell transformer out of circuit the first 2 times.....although pulling out the supply +ve should have done it !.. This time I took it completely off the wall.

My only thought is there's a guy in an upstairs flat with a blown bulb in his spare bedroom.... remember that episode from friends when they couldn't identify what a switch was for ?

One lesson I've learned is test again before getting the big hammer out !

Thanks for the help,

Al
 

Reply to Ring final fault - please help ! in the Australia area at ElectriciansForums.net

Similar Threads

Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi, my CDA FWC303 wine fridge is knackered. The compressor doesn't start and I've traced it to the PTC which I plan to replace and have identified...
Replies
2
Views
599
Hello all. I have just bought my first house but it needs a bit of work. I am re-wiring it and I've found the conservatory ring has been spurred...
Replies
11
Views
2K
Hi all, I had a fault on site today I've not encountered before. if anyone could shed some light on a similar fault they may have encountered...
Replies
9
Views
2K
A recent EICR turned up a fault: an RCD fused spur was feeding a socket and a shower pump, and neither socket or pump had continuity on the CPC...
Replies
17
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock