Discuss RISO seems low in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

S

silverpulser

Hi, I have a 16 panel 4Kw solar panel system which is now 4 years old. The inverter is an Aurora Uno and is configured with two strings (SW and SE facing roof elevations).

Recently my RISO in the mornings has dropped from an admittedly already lower than ideal 10Mohms to a new low of 3.2Mohms and 2.6Mohms over the last two days.

I know that Aurora say that anything over 1Mohm is OK but when installed and for a good while afterwards it measured 20Mohms.

Should I be concerned?

Shaun
 
if it keeps dropping then it indicates a likely problem, good to keep a note of the weather conditions when it's worst - ie if it's when it's wet / wet and cold / dry and sunny etc as that helps to narrow down the likely issue.
 
if it keeps dropping then it indicates a likely problem, good to keep a note of the weather conditions when it's worst - ie if it's when it's wet / wet and cold / dry and sunny etc as that helps to narrow down the likely issue.

The low readings followed a couple of days of light rain. Yesterday it had increased back up to 9.9Mo after a couple of fine days.
 

Reply to RISO seems low in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

Hi all. Long story short - my Aurora P-One developed the common E031 fault. I carried out the repair myself (ex electronics teacher), replacing...
Replies
0
Views
1K
Two Auroras 9 years old 3000 and 5000 with 4 strings total. Only 5000 has RISO LOW GIF Red problem. Even after switching strings between 3000 and...
Replies
0
Views
634
Hello Is it possible for solar panel monitoring to over state the actual power generated by the system? My friend’s 6.4kW system has generated...
Replies
3
Views
1K
Hi all, total newbie to the forum. I sincerely hope that those in the know-how would be able to assist me. On my semi-detached house we have an...
Replies
13
Views
2K
Hello all, I've just been perusing the AM2/E/S threads on here. Thought you might like a bit of a review. If, like I did, you find yourself...
Replies
7
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock