Discuss RLC Circuits - Phasors in the Canada area at ElectriciansForums.net

L

LearnerDave

Hi Guys,

Just wondering if anybody would mind explaining the main purpose of working out the lead/lag of current compared to voltage in RLC circuits?

Is it to do when selecting/derating cables for current carry capacity?
Is there any other things that happen? maybe extra heat build up in cables?
If there is a excessive lead or lag, can it affect any other circuits, if so what effects can it have?

Cheers Dave
 
Hi L'Dave
The problem with phasors in RLC circuits is to do with power
At unity the power in a
single phase circuit = Volts x amps
If it is an RLC circuit with a lead or lag
current the formula is
Power = Volts x amps x Cos (phi) The angle between the Voltage and the current
So for a circuit with a Power factor of Cos (phi) = 0.8
The power = Volts x Amps x 0.8
This means the current must be higher to give the same power output
Higher current means bigger cables overheating etc.

This is the reason discharge lighting power values are multiplied by 1.8
So an allowance is made if the Power factor correction (PF) equipment inside the fitting or luminaire fails
EG 10 x 70 watt = 700 watts x 1.8 = 1260 watts
Max Current for circuit i= corrected Power/Volts = 1260/230 = 5.4 Amps
If the PF equipment corrects to unity the actual current will be 700/230 = 3 amps
 
It's for a number of things, from working out the phase angle of each phase you can determine the current in the neutral, it also helps to work out the size of capacitors needed to bring power factor close to unity, if the power factor is low it increases the current which affects cable sizing etc, also the electricity bill provider puts additional reactive power charges on.

e.g using a 5KW motor and pf of 0.65 and 0.9
W/(1.73xVxpf) =A
5000/(1.73x400x0.65)=11A
5000/(1.73x400x0.9)=8A

You can see an increase in current from one motor, from a factory with 150 motors it becomes a little more critical, for the distribution network its a problem and i guess thats where the reactive power (KVar) charge comes from.
 
Last edited by a moderator:

Reply to RLC Circuits - Phasors in the Canada area at ElectriciansForums.net

Similar Threads

Hello All, I have just found out that a family member who is having some Building work done has been advised to insulate above the Kitchen...
Replies
16
Views
754
I’m running wires to the basement for future basement finishing. I’d like to add two circuits of outlets (one on the finished side and one on the...
Replies
0
Views
581
Hi All, I've installed a Lorex doorbell recently, but it is not turning on. I did some tests using a multimeter and this is what I found...
Replies
5
Views
1K
I have a 37KW motor and need to replace some burnt out 35mm2 tri rated cable(loose connection). I’ve looked at 25mm2 Tri rated cable the data...
Replies
6
Views
3K
Hello all, I have a question please concerning the calculation of the non-adiabatic factor for screen/sheath with a case that is not mentioned...
Replies
3
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock