Discuss safe isolation- the niceic way! in the Certification NICEIC, NAPIT, Stroma, BECSA Forum area at ElectriciansForums.net

J.C.E

-
Arms
Reaction score
158
niceic initial assessment tomorrow! woop woop

Seek permission to isolate
isolate, locked off with signage- keep key on you
prove my gs38 approved voltage indicators on a known source (will use supply side of main switch?)
test between L-N,L-E,N-E for voltage
re-prove voltage indicator on known source
precede with work with caution

I do not want to leave any holes for the assessor to pick at- so a few thing I want advise on-

1)OK to use main switch as my known source?

2) I am just using a lighting circuit I have installed as my job...

Turn off main switch before taking off cover?
Take cover off only isolate rcbo for the light circuit- leaving all other circuits on? whilst doing my testing on my circuit? -what about walking away from fuse board to do my r1+r2 in another room ect?


Any advise welcome

cheers guys
 
niceic initial assessment tomorrow! woop woop

Seek permission to isolate
isolate, locked off with signage- keep key on you
prove my gs38 approved voltage indicators on a known source (will use supply side of main switch?)
test between L-N,L-E,N-E for voltage
re-prove voltage indicator on known source
precede with work with caution

I do not want to leave any holes for the assessor to pick at- so a few thing I want advise on-

1)OK to use main switch as my known source? YES

2) I am just using a lighting circuit I have installed as my job...

Turn off main switch before taking off cover? YES
Take cover off only isolate rcbo for the light circuit- leaving all other circuits on? whilst doing my testing on my circuit? -what about walking away from fuse board to do my r1+r2 in another room ect?

Proper way to do it would be to turn off the whole board whilst you are in it, replace cover before live testing. Depends on your assessor though. If you leave the board that will be fine as it will be locked off.


Any advise welcome

cheers guys

......
 
and don't forget to PAT test the kettle before making the assole (crossed out) assessor a brew.
 
...When i need to re-test the operation of my voltage indicator,i use a choice of supply,that has remained uninterrupted,in my location,since the early eighties...:yawn:
 

Reply to safe isolation- the niceic way! in the Certification NICEIC, NAPIT, Stroma, BECSA Forum area at ElectriciansForums.net

Similar Threads

Hi everyone, When checking my consumer unit voltages with the full board off, I stumbled across something head scratching. Measuring the feed...
Replies
1
Views
615
Hello All and happy new year. Over the holiay I have changed all of my old sockets to some nice new ones and added a couple with usb sockets for...
Replies
4
Views
765
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi I am looking for advice please. Last week I done my am2. And the only thing I failed on was safe isolation of the 3 phase circuit. The...
Replies
11
Views
5K
Hi all, I have an unusual issue with a recent rewire I have just completed which I hope you guys can assist with. For background, this is a...
Replies
19
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock