12
Hi All

In the process of entering data for a recent EICR and could do with a little help to fill in a blank field ...

Short Circuit Current Rating for ... a Wylex 100A 100mA DP RCD BS4293 not time delayed.
I did look when on site, but couldn't spot it on the device, front or sides and don't fancy a long drive back to site to power the site down so I can disconnect it to check the back of it, besides something tells me it would be a wasted journey anyway.​

If anyone can help out with an answer, or can post a link to another forum where this has already been answered that would be very handy thank you ... sorry, but I can't find one, maybe I'm having a bad day using the search facility, but keeping my fingers crossed someone will be able to help.

Thanks
Paul
 
It's not a main switch within a DB, but an isolator in it's own enclosure in the meter tails.

Maybe I'm being a little ----, but there is a circuit from the meter to the RCD in question, then a circuit from the RCD in question to a set of service blocks that in turn feed a DB and isolator supplying a remote building.
 
The rcd is rated at 100A for continuous duty, what it is rated at for let through fault current would be different. Why don't you ask Wylex.
 
wrong terminology in my previous post . The rcd only detects earth leakage . It is not rated to disconnect faults of a ka rating .

What certs are you using ?
 
wrong terminology in my previous post . The rcd only detects earth leakage . It is not rated to disconnect faults of a ka rating .

What certs are you using ?
I maybe wrong but I disagree, I suspect it does have a maximum fault current rating.
 
Have emailed electrium who make Wylex but not sure when I'll get a reply as it was well.past office hours hence my asking here in case the wealth of knowledge could give me an answer sooner.

Thanks for feedback to date, will let you know what, if any, reply is forthcoming from Electrium/Wylex.

PIRform is the software in question.
 
Had a reply from the Wylex people within Electrium which was ...

"If the RCD is installed into one of our units it is tested to 16.5kA.

If it is a standalone item there are no ratings or tests for the RCD units."

So, there you have it from the horses mouth ... so to speak.
 

Reply to SCC rating ... in the Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock