Reaction score
1
I am currently doing a 3 hour duration test in Selfridges for the em lighting. When I turn off the mcbs the emergency lighting does not activate. I have asked if this is to do with the central battery system but the staff will not let me and my colleague touch it. Just wondering if anyone has had a similar situation and how they got around it.......
 
Have you been able to inspect one of the fittings as slave luminaries for central systems will contain no batteries nor will they have led charge indication or have you confirmed it is a central battery system.
 
Last edited:
can you give us some more i formation about the emergency lighting installation?
If it's a central battery system then you don't test it by running the lights for 3hours the same way you would self contained units.

However the emergency lighting, if non-maintained, should still come on with a loss of the supply to the normal lighting in the area.
 
I am currently doing a 3 hour duration test in Selfridges for the em lighting. When I turn off the mcbs the emergency lighting does not activate. I have asked if this is to do with the central battery system but the staff will not let me and my colleague touch it. Just wondering if anyone has had a similar situation and how they got around it.......
question, do you know what you are doing !
 
Ok since you were rude I will be too. **** you. I know exactly what I'm doing. **** off if you're not going to help

Unfortunately we only have your opening post to go by, which suggests that you are testing a central battery system by operating the emergency lighting for 3 hours.
Since you know exactly what you are doing you are obviously aware that this is completely the wrong way of testing a central battery system.
 
Looking at it from a different angle, so to speak, I am wondering if what the issue is that the emergency fittings are not illuminating when the local supplies are dropped out. From what little experience I have with central battery systems I would imagine that there should be a "power failed" type relay which is normally constantly energised by the local ccts but when they fail then it closes and energises the emergency fittings. I would imagine that if there is not a local relay then the emergency lighting only comes on where there is a wider power failure than a single cct or two or even one lighting board loosing its supply.
 
Only ever test the self contained emergency lights in pubs etc for the 3 hour duration. However I have seen them and when replacing lights, isolating circuits has caused a relay to operate and emergency lights in that area illuminate. Think you're knackered.
 
The control panel should have a test facility.
Reading between the lines, I think that the OP is not been allowed access to the panel.

But, out of curiosity, would it be normal to expect that on a central battery system there would be some method of detecting local supply failure? By that I mean to replicate the way that self-contained fittings are normally wired on the same circuit as the lights that they are providing replacement illumination for.

(My only experience with central battery systems is as totally separate systems where the outputs are switched on when the building is open to the public, all the fittings are illuminated in addition to local fittings so there is no need for any switch over on any scale of power fail)
 

Reply to Selfridges Emergency battery test in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I tested a self test emergency lighting with three gears .While testing 2 of the gear doesn't passed 3 hour test but 1 Did Wit the same battery ?Why?
Replies
6
Views
744
Hi I'm in need of some advice. First of all i'm not an electrician but do have an understanding of electrics as i come from an electronics...
Replies
4
Views
602
Hi guys, Been asked to fit 2 lights and a switch, which in reality turned out to be rewiring a multiple PIR setup to a single switch, adding...
Replies
0
Views
824
Hi guys, Been asked to fit 2 lights and a switch, which in reality turned out to be rewiring a multiple PIR setup to a single switch, adding...
Replies
0
Views
634
Hello fellow sparks, I’m looking to do my testing and inspection course which starts on the 30th of April, but I have not got much testing...
Replies
0
Views
227

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock