Hi Guys,
Looking for a little advise regarding installation of new supply to feed a communal shower block at a caravan site.

The shower block will have 7x 8.5Kw electric showers, 2x 2Kw over-sink instantaneous water heaters, a couple of frost guard heaters and lighting with a couple of extractors. In total i calculate the max load to be just shy of 65Kw.
25mm 4core SWA has already been run back to the supply on recommendations by another electrician.
The problem I have is what size breaker to fit at the supply end ...
Most standard load 3 phase boards only allow a maximum rating of 63A for the MCBs and I know that this will be too small for the shower block.
I've calculated the max load as everything on at the same time due to the fact that the shower block will be used during both summer / winter.
The way I see it, everybody could all turn up at once to shower/wash so I can't really justify using diversity.
Based on this, I'm thinking that the submain will need to have overload protection of over 80A.

Any help would be great,

Thanks guys ...
 
in that case fit a KMF with 80A fuse. what's the earthing arrangement?

65kW eqwuates to 270A before diversity. some serious calculations needed here.
 
oops. just seen the 3 phase bit. now it makes sense. ignore my last post. as richard pointed out, a 3 phase switch fuse with 80A fuses will do the job.
 

Reply to shower block supply in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

hi guys / girls , any advice would be appreciated, So the situation is a domestic property has a 3 phase supply , from the service head we have 3...
Replies
1
Views
262
I'm in the middle of preparing a quote for installing 12 x 3Kw and 4 x 2Kw halogen heaters in a church. The system design was provided by a...
Replies
27
Views
965
Just to highlight how wicked people can be. This set up was bad enough. House is just bought from deceased estate. Typical '30s house. See the old...
Replies
8
Views
1K
Been looking at a CU change in a small office and would appreciate comments on the following. Office is supplied from the mains intake in the...
Replies
52
Views
6K
Hi all, I have a regular client who has asked for a battery back up system to be installed at their home. They live in a rural location on a...
Replies
2
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock