  1. sparksburnout

    sparksburnout Electrician's Arms

    Location:
    Notts
    Yup, nice one.
     
  2. to hide this advert.
  3. westward10

    westward10 Electrician's Arms

    Top Poster Of Month

    Location:
    Northamptonshire
    Most sparks reading a Report with it as a C3 would think nothing of it.
     
  4. Andy78

    Andy78 Trusted Advisor

    Location:
    Kingston upon Hull
    A note with no code would be the furthest i would go.

    I use the logic that the EICR is a technical report as to the safety of an installation based on BS7671. If it is compliant with BS7671 in all ways it cannot warrant a code.
    If I put a code based on my opinion against something that is compliant with BS7671 , the report ceases to be based on BS7671 and becomes open to abuse.
     
    DPG, hightower, Spoon and 1 other person like this.
  5. sparksburnout

    sparksburnout Electrician's Arms

    Location:
    Notts
    Good point. Personally, I have not come across this scenario. As you say, there is no actual contravention. Also, as Westie says, no other Spark reading it is going to get in a stew. At the end of the day the report will be Satisfactory so the Landlords and agents won't look any further. Maybe a written recommendation, attached to the report would be the best way to do it as you say.
     
    Andy78 likes this.
  6. Pat H

    Pat H Don't ask, get an Electrician in.

    Location:
    Ware Herts
    Business Name:
    Sparks of Intelligence
    As others have said if its BS7671 compliant then you can't issue a code, even a C3.
    I'd probably verbally suggest an isolator and email that as well as a recommendation but not include it in the EICR
     
  7. Murdoch

    Murdoch Electrician's Arms

    Location:
    Woking
    As the inspector you can offer your opinion of the installation, and in this box I would include such a comment
     
    DPG, sparksburnout and Andy78 like this.
  8. sparksburnout

    sparksburnout Electrician's Arms

    Location:
    Notts
    Nice to see the OP coming back with some comments or constructive thoughts......
     
  9. Murdoch

    Murdoch Electrician's Arms

    Location:
    Woking
    At the time of posting this he was viewing this very thread 6 minutes ago.... maybe he's composing an update!
     
  10. yellowvanman

    yellowvanman Electrician's Arms

    Location:
    Dorset
    Not sure what you guys want me to add. I've said what I will probably do in post #10. Didn't quite manage to complete all tests yesterday so have to return one day next week, which gives me time to ponder some more!

    Will probably include it in the observations but without a code. That way I've mentioned it but it won't affect the satisfactory/unstaisfactory conclusion.

    Could extent this discussion further by the fact that the installation only has RCD protection on 1 circuit - on the shower which appears to have been added after the refurb was completed about 20 years ago. Flat is on the first floor. Discuss!
     
  11. sparksburnout

    sparksburnout Electrician's Arms

    Location:
    Notts
    Oh hold on
     
  12. 7029 dave

    7029 dave Trusted Advisor

    Location:
    bedfordshire
    Yellow, you are the guy on the job, if you feel to put a code 3 in, that is absolutely fine, it is only a recommendation, still satisfactory on the report. That would be my take only because that is my opinion, because I like local isolation.It will be up to the client at the end of the day.
     
  13. sparksburnout

    sparksburnout Electrician's Arms

    Location:
    Notts
    Why do we need to discuss it? Your doing the EICR? You challenged me that I was doubting your professional ability.
     
  14. yellowvanman

    yellowvanman Electrician's Arms

    Location:
    Dorset
    I just thought I'd let you guys mull that over! I'm sure there will be different opionions out there!

    Ok, I'll start with my take. Plenty of C3's, lack of RCD protection on bathroom circuits (light + heater), no RCD protection for concealed cables, no RCD protection on sockets. The only possible C2 could be lack of supplementary bonding between shower/heater/lights in bathroom, but since the consumer unit is in the adjacent airing cupboard I suspect resistance between circuit earths will be OK, but will check!
     
  15. to hide this advert.
  16. sparksburnout

    sparksburnout Electrician's Arms

    Location:
    Notts
    You mean, you want the forum in general to instruct you as to how to do your job? You are undertaking an EICR, it's a tricky old number requiring quite a lot of things, experience, qualifications and so on. Have you got any?
     
  17. yellowvanman

    yellowvanman Electrician's Arms

    Location:
    Dorset
    I don't want the forum to instruct me in anything I've just told you want I'm going to do, but I know others will disagree and thats their perogative.

    As for experience and qualifications I probably have more than you!

    I'm now leaving this thread with no further input!
     
  18. Murdoch

    Murdoch Electrician's Arms

    Location:
    Woking
    C2 for the lack of RCD protection on the sockets for me.........
     
  19. sparksburnout

    sparksburnout Electrician's Arms

    Location:
    Notts
    Oh dear well that's an awful shame. It just seemed to me that every time you get a bit of a problem you come on here and ask how others would tackle it, not the sort of form for one which such an impressive pedigree? Maybe it's just me....
     
  20. 7029 dave

    7029 dave Trusted Advisor

    Location:
    bedfordshire
    I don't think there is any need Sparks to rip into the guy, we all here to share our experiences and OPINIONS. Listen to uncle Dave.
     
    Dave OCD, Hellmooth and telectrix like this.
  21. GMES

    GMES Chief Gorilla Staff Member Trusted Advisor

    @yellowvanman and @sparksburnout , not sure what the beef is with you guy's if there even is one but lets keep it professional and out of the thread.
    Cheers.
     
  22. telectrix

    telectrix Scouser and Proud of It Trusted Advisor

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    as for me, i've had enough of bloody showers. rain all week, getting soaked just getting gear off van, bugger it. time for beer.
     
    GMES likes this.
Loading...
Similar Threads - Shower isolator Forum Date
shower block supply Commercial Electrical Talk Mar 18, 2017
wet room shower trays Tiles - Advice on installing and buying tile Mar 8, 2017
Sealing around a shower tray Tiles - Advice on installing and buying tile Mar 6, 2017
10.8Kw shower on 6mm² T&E Electrical Forum Mar 1, 2017
Ventilation Of Shower / Bathroom - What Would You Suggest? Tiles - Advice on installing and buying tile Feb 27, 2017
shower supplies Electrical Wiring, Theories and Regulations Feb 23, 2017
No Spare Way for Shower Can Move Doorbell to Share Lighting Circuit or put Doorbell on Switch Spur? Electrical Forum Feb 22, 2017
Tanking a separate shower Tiles - Advice on installing and buying tile Feb 22, 2017
Insulation test on shower with neon switch Electrical Forum Feb 19, 2017
Is best to fit the shower screen bracket to the wall or too the tiles Tiles - Advice on installing and buying tile Feb 18, 2017