P

Piratepete

A farmer client has a supply cable going underground from the DNO's kennel to a large barn converted to stables with power and light. The cable is fed from a 30 Amp switch fuse and a preceeding 30 mA RCD.

In the barn, I noted that though the power and light were on separate 2.5mm and 1.5 mm circuits these were connected together to the incoming cable by a large choc block wrapped in insulating tape! There's a separate 6mm earth wire also into said block (TT supply).

So on replacing this little mess with a 2 way garage unit I discover that the supply cable is not a 2 core SWA that it looked like, but is single core aluminium with a stranded copper insulated outer sheaf which is being used as the neutral conductor.

Does anyone recognise this type of cable and know it's normal use please?
How do I work out it's current rating?
Can I leave it? Ever tried getting a farmer to spend money on something that's been working fine for years!

Further info. It's stamped Crompton 600volt. IR to earth is 930Meg for inner core but only 3Meg for the outer neutral (NO surprise!).

Pete
 
sounds like concentric cable.
de95437ecdce938c43e157cd4bba79fb.png
 
Last edited:
Hi Lee
Yes, it is concentric but never come across it before in my sheltered 'Domestic' life. The core is at least 16 sq mm, so no doubt good for 30 Amps. But it's installed under a concrete yard. Suppose it's ok if it's mecanically protected in a duct but all I can see is it disapearing into solid earth!
 
Hi Lee
Yes, it is concentric but never come across it before in my sheltered 'Domestic' life. The core is at least 16 sq mm, so no doubt good for 30 Amps. But it's installed under a concrete yard. Suppose it's ok if it's mecanically protected in a duct but all I can see is it disapearing into solid earth!

Yeah not ideal from the regs POV but the DNO bury it all the time.
 
Last edited:
Yeah there will be literally thousands of miles of the stuff buried all over the country - should be in ducting but often isn't continuously to say the least ! I've seen it buried direct around 75mm below a road surface before ! :yesnod:
 
Hi Lee
Yes, it is concentric but never come across it before in my sheltered 'Domestic' life. The core is at least 16 sq mm, so no doubt good for 30 Amps. But it's installed under a concrete yard. Suppose it's ok if it's mecanically protected in a duct but all I can see is it disapearing into solid earth!

No it is not suitable for burial, or even any use, within a consumers installation.
It does not have an earthed metallic armour, nor does it have any earth conductor. This cable is only suitable for use in a TNC system, which it is illegal to install in a consumers installation under the esqcr
 
Last edited:
No it is not suitable for burial, or even any use within a consumers installation.
It does not have an earthed metallic armour, nor does it have any earth conductor. This cable is only suitable for use in a TNC system, which it is illegal to install in a consumers installation under the esqcr

Try telling that to all the DNOs in the country Dave. :p
 
No you know what I mean, they bury it everywhere on the distribution network.

I don't know what you mean, no.

Concentric cable such as this is not suitable for burial in a consumers installation but is suitable for burial in a DNOs installation. The difference is quite obvious is it not?

For direct burial of a cable an earthed metallic screen or armour is required, in a concentric cable such as this that can only be achieved by connecting the outer conductor as a protectively earthed neutral (PEN or combined neutral and Earth CNE) this would be a TNC system.
Within a consumers installation it is not permitted to use a TNC system therefore this cable cannot be used. Within a DNOs installation a TNC system is permitted and is widely used so this cable is suitable.
 
Most Utilities have fairly good network plans showing location of cables/pipes etc but they're never 100% accurate.

Edit - in reply to 7029 Dave's post.
 
Last edited:
I don't know what you mean, no.

Concentric cable such as this is not suitable for burial in a consumers installation but is suitable for burial in a DNOs installation. The difference is quite obvious is it not?

For direct burial of a cable an earthed metallic screen or armour is required, in a concentric cable such as this that can only be achieved by connecting the outer conductor as a protectively earthed neutral (PEN or combined neutral and Earth CNE) this would be a TNC system.
Within a consumers installation it is not permitted to use a TNC system therefore this cable cannot be used. Within a DNOs installation a TNC system is permitted and is widely used so this cable is suitable.

My whole point was you said it was not suitable for burial Dave, simple as that. And in the case of a TNS supply the cable would be split concentric so only a part of the outer cable circumference would be earthed below the outer sheath.
 
My whole point was you said it was not suitable for burial Dave, simple as that. And in the case of a TNS supply the cable would be split concentric so only a part of the outer cable circumference would be earthed below the outer sheath.

Only in the same way as you have just said 'not suitable for burial' if I was to quote you without using your full sentence.
The sentence, which you only highlighted a part of, stated that it is not suitable for burial in a consumer's installation. You have deliberately misquoted me

Split concentric is not under discussion here, but even if it was then it would also not be suitable for direct burial in a consumers installation as the earth only covers approximately a quarter of the circumference of the cable.
 
Last edited:
Only in the same way as you have just said 'not suitable for burial' if I was to quote you without using your full sentence.
The sentence, which you only highlighted a part of, stated that it is not suitable for burial in a consumer's installation.

Split concentric is not under discussion here, but even if it was then it would also not be suitable for direct burial in a consumers installation as the earth only covers approximately a quarter of the circumference of the cable.

We're still going round in circles, my point was that distribution rules are very different to the consumers side of things.
 
We're still going round in circles, my point was that distribution rules are very different to the consumers side of things.

Yes, and needlessly,

I clearly made the distinction that I was commenting on consumer's installations, as that is at we are concerned with on this forum and specifically in this thread.
You have then deliberately misquoted me and derailed the thread in what appears to be an attempt to make a point which did not need making in the first place.
 
Jesus, is this the 5 minute argument or the 10 minute one? Dave OCD is making the point that the DNO see fit to bury concentric cable directly, right up to and on to the customers premises. We all know what he means. Daz
 
A farmer client has a supply cable going underground from the DNO's kennel to a large barn converted to stables with power and light. The cable is fed from a 30 Amp switch fuse and a preceeding 30 mA RCD.

In the barn, I noted that though the power and light were on separate 2.5mm and 1.5 mm circuits these were connected together to the incoming cable by a large choc block wrapped in insulating tape! There's a separate 6mm earth wire also into said block (TT supply).

So on replacing this little mess with a 2 way garage unit I discover that the supply cable is not a 2 core SWA that it looked like, but is single core aluminium with a stranded copper insulated outer sheaf which is being used as the neutral conductor.

Does anyone recognise this type of cable and know it's normal use please?
How do I work out it's current rating?
Can I leave it? Ever tried getting a farmer to spend money on something that's been working fine for years!

Further info. It's stamped Crompton 600volt. IR to earth is 930Meg for inner core but only 3Meg for the outer neutral (NO surprise!).

Pete

Forget all the hair splitting nonsense being spouted, all you've done is install overcurrent/fault protection to the final circuits supplied by this cable. You have not altered the distribution circuit in any way. Note on your EIC that the distribution circuit does not comply with bs7671 and you recommend it is replaced. However it may be considered safe for continued use as long as a test and inspection is carried out yearly. --- covered.
 

Reply to Single Core 230Volt Supply?? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Background: I am not an electrician, I am a retired professional engineer high power broadcast transmitter design , but am dabbling outside my...
Replies
15
Views
2K
Hi I've inherited a very tight space, a KMF switch and some split-con for a sub-main to try and tidy up. It's a joyous non-restrained single...
Replies
3
Views
141
5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Replies
2
Views
491
So, the actual job is on a farm. I think I'll keep things simple at the moment and just ask about voltage drop. I'll come on to earthing and...
Replies
11
Views
2K
I've come across a DNO installed (SSEN) 3 Ph 3 core PNE supply cable from a private substation to a large Lucy domestic head. Cable 3 Ph is copper...
Replies
15
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock