Hi,

I am pricing for a new build property and the schedule of works shows the system as

  1. Provide and install an automatic fire detection and alarm system inaccordance with BS 5839: Part 1 to L3 standard. Electrician to provideon completion a wiring certificate confirming that the wiring to smokealarms conforms to the current I.E.E regulations. A copy of thiscertificate is to be forwarded to inspecting authority.





On the electrical drawings it shows it as a standard domestic system - heat in kitchen, smoke on landing/hallway - standard stuff.

I haven't been on commercial sites for a long time but L3 is a commercial fire alarm isn't it?

Many thanks

Dave
 
Hi,

I am pricing for a new build property and the schedule of works shows the system as

  1. Provide and install an automatic fire detection and alarm system inaccordance with BS 5839: Part 1 to L3 standard. Electrician to provideon completion a wiring certificate confirming that the wiring to smokealarms conforms to the current I.E.E regulations. A copy of thiscertificate is to be forwarded to inspecting authority.




On the electrical drawings it shows it as a standard domestic system - heat in kitchen, smoke on landing/hallway - standard stuff.

I haven't been on commercial sites for a long time but L3 is a commercial fire alarm isn't it?

Many thanks

Dave

http://www.aico.co.uk/What-do-I-fit.html
 

Attachments

  • smoke.PNG
    92.5 KB · Views: 55
Last edited:
You should clarify this if it is a domestic premises as not only is L3 non-domestic, but in fact all of BS 5839-1 is non-domestic.

BS 5839-6 is domestic. As stated the categories are LD rather than L in Part 6 to signify that they are for dwellings.

Hi,

I am pricing for a new build property and the schedule of works shows the system as

  1. Provide and install an automatic fire detection and alarm system inaccordance with BS 5839: Part 1 to L3 standard. Electrician to provideon completion a wiring certificate confirming that the wiring to smokealarms conforms to the current I.E.E regulations. A copy of thiscertificate is to be forwarded to inspecting authority.




On the electrical drawings it shows it as a standard domestic system - heat in kitchen, smoke on landing/hallway - standard stuff.

I haven't been on commercial sites for a long time but L3 is a commercial fire alarm isn't it?

Many thanks

Dave
 
You should clarify this if it is a domestic premises as not only is L3 non-domestic, but in fact all of BS 5839-1 is non-domestic.

BS 5839-6 is domestic. As stated the categories are LD rather than L in Part 6 to signify that they are for dwellings.

Fire alarms in dwellings - IET Electrical

LD3 is perfectly compliant for standard domestic installs. I have fitted LD1 in domestic situations where the builder made a drastic mistake.
 
Not a very clear spec and not a lot of information on the building use and layout

I'm thinking if the building is flats with communal areas then system is intended to be to BS5839 part 1 because of number of floors or other factors. Without a proper fire risk assessment in place it would be silly to make any assumptions without seeking further clarification from the client
 
thanks for info everyone.

I think the schedule of works info is wrong imho as its tiny 1 bed domestic bungalows. I have a detailed electrical drawing and this shows 1 heat and 1 smoke in each.
I was just unsure of the L3 reference. I'll clarify this with client tomorrow.

many thanks
 
Fire alarms in dwellings - IET Electrical

LD3 is perfectly compliant for standard domestic installs. I have fitted LD1 in domestic situations where the builder made a drastic mistake.

I didn't say it wasn't. I said that L3 is not a domestic fire detection and alarm system. LD3 and L3 are not the same thing.

Incidentally, it is overly simplistic to state that LD3 is acceptable. In Ireland - both north and south - a minimum of LD2 is required. Scotland may also be similar.
 

Reply to smoke alarm grades new build. in the Security Alarms, Door Entry and CCTV (Public) area at ElectriciansForums.net

Similar Threads

Having a bit of a mare at the moment with a small 2 story HMO (6 single rooms with shared kitchen) which was fitted relatively recently (2016 or...
Replies
18
Views
2K
Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
Replies
11
Views
2K
Hello all, Firstly, I am not installing this myself and have several pros coming in to quote in the new year. A couple of years ago, most of the...
Replies
3
Views
1K
Am I correct in thinking under the 18th edition for a new build property an AFDD is compulsory or is this not the case if risk assessed? I am...
Replies
5
Views
8K
Hi Im working in a staffed residential home (for severe learning difficulties/disabilities residents) they have a new onsite tanked gas supply...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock