Hi.. All
I am in the process of rewiring a house with a sizable extension for a kitchen dining room, I am going to install hard wired alarms, obviously one on the landing ceiling upstairs, one on the hall ceiling down stairs. My question is....... the ceiling in the extension has a high pitch ceiling rising to approx three metres with a small level surface at the top. I'm thinking it should have three alarms hard wired, the third being at the higest point downstairs. If there were to be a kitchen fire, the smoke would accumalate at this point before it reached the hallway which has two doors between the kitchen. I asked an old coleague of mine, he reckons that if the alarm sounds near the kitchen at the highest point, the customer wouldn't be able to silence it because they can't reach it... But I said, surely because they are interlinked you would be able to silence any one of them..He couldn't say and I'm not 100%. Any input appreciated. I will be installing three, I just want to be sure that it can be silenced on any. Thanks.
 
If it's a pointed ceiling (pitched), like you might get in a loft conversion, then the smoke detector must be at least 600mm vertically below the point of the pitch. The top 'triangle' would be "dead air" in the event of smoke moving around.

I would suggest you follow the same rule for your heat detector. But why not ring Aico tech help for advice?

If you need to "hush" the alarms then you need to hush the one that set off the alarm. Therefore it needs to be reachable.

They should also all be within reach (perhaps by using a handle or standing on a chair) so the test button can be pressed and so the back up batteries can be changed as required.
 
The smoke should be sited 900mm horizontally from the peak so probably would be out of reach anyway.

Smoke alarms that are out of reach can be units with non replaceable lithium batteries and also the 'smoke switch' I mentioned has hush, test & locate facilities on it for this very reason.
 

Reply to Smoke detctor/alarms in the Security Alarms, Door Entry and CCTV (Public) area at ElectriciansForums.net

Similar Threads

I'm about to order this wired smoke alarm system as it can network but I just went to see how my existing fire alarms are hooked up and there...
Replies
12
Views
1K
any BS 5839 experts know whether CO alarms should be connected to the smoke/heat alarm system ? after completing an efixx CPD it seems they should...
Replies
10
Views
1K
We have a domestic fire alarm system in some leasehold properties. The existing BRK alarms are no longer available in the UK. These alarms/system...
Replies
19
Views
2K
I currently have a home with 7 interconnected, hard-wired smoke detectors. I have a hard-wired heat alarm in the garage that I need to have...
Replies
4
Views
1K
Hi All, Please may I ask if light fixtures must now always be fitted by an electrician? also for domestic homes, is it okay for there to be a...
Replies
4
Views
767

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock