Fresh back from a few days away, I'm tempted to ask "so would normal cable be flame propagating ? "
Fire rated cables I get, but is that the same as non flame propagating ?
May need to duck off back to Heidi Land :)
 
Think people are so blinded by Am 3 and fire resistant fixings they ignore the requirements for cable systems on escape routes and T&E most certainly would not comply even if it were fixed with indestructible clips. Comment frequently when doing FRAs on this type of thing.
 
Reading that 422.2.1, towards the end it does say for BD2/3/4 the wiring systems shall be fire rated... (edit : just read Ian post #24 )
I did set fire to a cable to see what happened - not as bad as I'd hoped thought with the cable self extinguishing within about 10sec. Not surprising it failed IR testing after meeting Mr Rothenberger. Now for the pics :)

IMG_0637.JPG
 
Reading that 422.2.1, towards the end it does say for BD2/3/4 the cables shall be fire rated...
I did set fire to a cable to see what happened - not as bad as I'd hoped thought with the cable self extinguishing within about 10sec. Not surprising it failed IR testing after meeting Mr Rothenberger. Now for the pics :)

View attachment 36346
Try that with LSOH cable which is non fire propagating and will not give off the fumes standard twin & earth will
 
FP200 not used for smoke detectors- C2

Had no regulation reference or anything
I would contact them and ask their reasons. A Grade D system does not need fire resisting cable unless the requirements of BS7671 could only be met by doing so. I find it unlikely, though not impossible the reason is for an inappropriate wiring system on an escape route. More likely they have misread BS5839-6 or confused it with BS5839-1, the fact they have given a Code 2 is neither here nor there and it would be interesting to know why they have picked up on it to resolve your problem.
 
Reading that 422.2.1, towards the end it does say for BD2/3/4 the wiring systems shall be fire rated... (edit : just read Ian post #24 )
I did set fire to a cable to see what happened - not as bad as I'd hoped thought with the cable self extinguishing within about 10sec. Not surprising it failed IR testing after meeting Mr Rothenberger. Now for the pics :)

View attachment 36346

fire will tend to travel upwards rather than down so you have it biased towards self extinguishing there. If you did it again but set fire to the bottom of a vertical section of cable you might get it to burn a bit longer.
 
We are going off in a tangent here..lol
Domestic fire detection must meet BS5839 part 6 & BS 7671. Grade D can be wired from the consumer unit or from a local light fitting, in normal T&E. If specified then LSOH. As with emergency lighting, the units contain back up batteries. So the cable is sacrificial. The units also require a screwdriver to remove from the base, giving total isolation from mains, complying with the lockable isolation rule. Grading such as A,B,or C utilize a central psu, or control panel so the cable now becomes and issue to supply as long as possible. So here FP or Pyro would be required.
 

Reply to Smoke Detector Wiring in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I need your help please once again in tracing a fault. Am DIY but not clueless. Converting former kitchen into 2 rooms: bathroom and laundry. The...
Replies
24
Views
2K
Hi all Recently we've been having a few issues with smoke and heat detectors.. been fitting them for years and years now mostly without any...
Replies
14
Views
2K
Not come across this before, so would like some help, please. I went to install smokes and heat alarm (to new Scottish regs) in a fairly modern...
Replies
2
Views
1K
Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
Replies
11
Views
2K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock