Hi,

Quick question, does anyone know if there is a different spec to the U.K. for earth rods?

I'm told in Spain they are longer but not sure if that is correct? Also are there any regs in Spain relating to the positioning of the rods etc (i.e. distance fro property)?

Any advice greatly appreciated as I am new to this forum. :)
 
There are myths and tales about different nationalities having varying average rod sizes, apparently the average size in Japan is smaller and the average size in some African countries is fabled to be enormous and also supposedly of a larger diameter. ;)

Seriously though, the specs of an earth rod are about its impedance which we refer to as its Ra measurement. In certain ground you need a longer rod to achieve a target impedance than in other types of ground. Factors such as moisture content, conductivity of the soil, overlapping zones of influence, whether the ground freezes and whether you hit the water table would affect how long and earth rod you would need. Also whether you are providing additional protection in the form of an upfront RCD would possible influence how low your rod impedance needs to be.
 
Last edited:
There are myths and tales about different nationalities having varying average rod sizes, apparently the average size in Japan is smaller and the average size in some African countries is fabled to be enormous and also supposedly of a larger diameter. ;).

Maybe the spanish fly will extend its potential and increase leakage to an acceptable level
:joker:

Back on topic I know little about Spains electical instalations so cannot advise sorry.
 
spanishrods need to be longer to achieve results as they sleep from 12 noon till 4 p.m.
 
Normally minimum specified by local council but you may have to put 4 in to get the required reading. The reading must be noted of the cert (Boliten) which needs to be issued by a registered Electrician. In on town where i work Spikes are 1.5m go up the road 3km and its 2m. Yes there are many regs regarding TT installs.
 
Last edited by a moderator:
Every install has RCD protection Marvo. Also different rules for different comunidads (counties) the norm is 1.5mm just depends how many it takes to get decent Ra.
There are myths and tales about different nationalities having varying average rod sizes, apparently the average size in Japan is smaller and the average size in some African countries is fabled to be enormous and also supposedly of a larger diameter. ;)

Seriously though, the specs of an earth rod are about its impedance which we refer to as its Ra measurement. In certain ground you need a longer rod to achieve a target impedance than in other types of ground. Factors such as moisture content, conductivity of the soil, overlapping zones of influence, whether the ground freezes and whether you hit the water table would affect how long and earth rod you would need. Also whether you are providing additional protection in the form of an upfront RCD would possible influence how low your rod impedance needs to be.
 

Reply to Spanish Earth Road installation in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Good morning everyone. I’m looking at getting an EV charger installed at my home and the company is requesting that I earth bond my water supply...
Replies
8
Views
4K
I have completed the 2919 course and was told during this that all chargers would require a TT connection, whether solely for the charger or as...
Replies
61
Views
9K
Hi, just a quick question... I’m at the stage now where I’m being pretty nosey at other people’s consumer units/supply set ups etc to further...
Replies
6
Views
1K
Hi, This is my first post, it is a bit long but I felt a full explanation is necessary. I am a competent DIYer and I live in the South of France...
Replies
16
Views
2K
Hello, I am a Trainee here on the Forum. I am seeking some further advice/input on a specific technical matter of importance to me. Briefly, I...
Replies
12
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock