hi i have a customer whos rcd trips sporadically.
maybe twice per month
its been going on for 12 years!
customer has had enough.

1 ring down
2 ring up
3 cooker
4 shower
5 garage

no damp walls
no known damage to cables
no specific time of day

fridge is approx 12 years old

i know the normal tests
rcd ramp
rcd x1 x5 x.5 etc
r1 rn r2
ins resi

do you guys use any specific rcd tests to establish where the fault lies?

cheers in advance
:cool:
 
Get an earth leakage clamp meter and test the appliances. I would start with that 12 year old fridge, it might have something to do with that 12 year old fault?
 
could always try a PAT on the fridge if e/l clamp meter not availabe.
 

Reply to specific rcd tests in the Australia area at ElectriciansForums.net

Similar Threads

Hi Have a nightly problem - will be changing a consumer unit however have a problem customer has an older mem m6 32amp rcd/mcb on downstairs ring...
Replies
10
Views
4K
I have just popped out to a frustrated customer who has had intermittent tripping of a 30mA RCD for years, on average 5 - 10 x p/month. It used to...
Replies
31
Views
4K
Here's a weird one.. customer complains of sporadic rcd tripping some time ago so I do a series of tests, only thing on rcd are skts and lights...
Replies
17
Views
2K
Doing one more of the flood of EICR today on a rented property before a tenant change, but ran into a slightly interesting case so would...
Replies
71
Views
13K
Plumber changes boiler and RCD main switch starts tripping at various times when its firing up or soon after. (I was there doing other work). I...
Replies
18
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock