Discuss Spur from a spur in the Australia area at ElectriciansForums.net

S

Steve D

Greetings all, and a Happy new Year !

Regarding (unfused) spurs, can anyone offer some guidance please.

I used to think that it was a cardinal sin to spur from a spur (unless you use a fcu) and I'm sure the regs (haven't got my regs to hand so can't quote the reg) says somewhere that an unfused spur can supply only a single or a twin socket.

However, the diagram they have of a typical radial final circuit in the appendices (Appdx 15 ?) shows an unfused spur feeding an additional 2 sockets.

Is this just an error in the diagram ?

Also, can you clarify exactly what is meant when they say "an unfused spur may be connected to the origin of the circuit in the consumer unit."

They're talking about the origin in the consumer unit, but surely they're not saying you can run a parrallel circuit (albeit only a single or twin socket) on the same breaker are they? That's the only way I can interpret that statement, but I thought that in other places in the regs they make it perfectly clear that each circuit needs it's own protection device.

Also, is there a difference in spurring from a socket and spurring from a junction box ?

Regards
Steve
 
If you look at the diagram the cable is 4.0mm and not 2.5mm for a 32a CPD.

Here is a link to a update which came out in July IEE Wiring Regulations updates - The IET
 
Last edited:
I see what you're saying regarding the radial diagram on the right hand side "An unfused spur run in 2.5 mm2 cable should feed one single or one twin socket-outlet only."

However looking at the radial diagram on the left hand side it clearly shows 'all live conductors' as 2.5mm2 and it shows spurring from a spur?
 
I see what you're saying regarding the radial diagram on the right hand side "An unfused spur run in 2.5 mm2 cable should feed one single or one twin socket-outlet only."

However looking at the radial diagram on the left hand side it clearly shows 'all live conductors' as 2.5mm2 and it shows spurring from a spur?


Yes but look at what the protective device for the circuit that one is 20A for 2.5mm spur off spur and the other is a 32A device for 4.0mm off 4.0mm, it all comes down to the current carrying capacity of the cable.
 
As far as spurring from the origin of the circuit in the CU goes, I take that to mean that you can run a spur from the SAME CU TERMINALS as the circuit you intend to spur from, rather than spur out of an existing socket on the circuit. Its a way of adding a spur without breaking into an existing circuit, but it still counts as a spur on that circuit.
Useful to know......
 
Hey there.

When I was doing my training my old lecturer used to say to me there's 3 places you can spur from on a ring.

1. from an existing socket
2. from a joint box
3. from the mains board itself i.e off the same breaker.

If i spur off to a new twin socket I always use 4mm but, if only a single then 2.5mm.
 

Reply to Spur from a spur in the Australia area at ElectriciansForums.net

Similar Threads

DIY'er question: I have a singe switched fused spur above my kitchen counter, providing power to an undercounter fridge socket beneath it. The...
Replies
2
Views
386
We have an outdoor socket that is hard wired into the ground floor power circuit and protected with an rcd in the consumer unit. I now plan to add...
Replies
17
Views
3K
DIYer question. I have a 32 amp supply going from consumer unit in garage to kitchen. It supplies an induction hob only. The cable is easily...
Replies
34
Views
3K
Hi Guys, Long time member and not a regular user here. I do pop in here when the odd unknown pop's up and unable to locate an electrical dilemma...
Replies
4
Views
851
Good Evening. I’m currently carrying out an EICR. I have a cooker circuit radial with a 32amp mcb fed from and RCD split board. There is a 45amp...
Replies
14
Views
793

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock