Sorry mate I couldn't resist It meant you are welcome, I only did it to torment you.
 
Because I didn't get a reply two days ago, as to if the proposed circuit would be safe, I destroyed the wallpaper and chased the walls and put in a ring without any spurs. Well got the cable in, not wired it up yet!!

That looks like you're installing a new circuit now.

I have seen the diagram in section 15 of the BYB, can anyone please explain to me why this circuit would not conform to BS7671

View attachment 34344

No one can possible tell you if that circuit complies with the current regs, it's just some squiggly lines.
What's the ocpd? is there rcd protection? what's it wired in? is all main bonding in place? and more.
And as stated already, you will need to test your work and issue the relevent c
 
I have seen the diagram in section 15 of the BYB, can anyone please explain to me why this circuit would not conform to BS7671

Reg 433.1.204

(i) Locate socket-outlets to provide reasonable sharing of the load around the ring.

Your diagram has all the spurs located on one part of the ring not shared around the ring.
 
Can people stop using acronym's please, what is a BYB?
Get used to it. Every trade and profession has its own specific lingo. Just ask or Google if you don't know.

Here's a few for you to look up before the next lesson. Hint: there's a list of abbreviations in the BYB.
DNO, ELV, SELV, RCBO, RCCB, FCU, BC, CPC, DB, GLS, IR, MFT, PIR, RFC, SES, SWA, UKPN
 
Reg 433.1.204

(i) Locate socket-outlets to provide reasonable sharing of the load around the ring.

Your diagram has all the spurs located on one part of the ring not shared around the ring.


You cannot possibly know if the load is balanced, It is impossible to work out, we do not know what appliances will be plugged in, so that regulation is irrelevant regarding this design.

The regulation states sockets, not spurs.


There are 3 sockets either side of the 2nd section of the ring. It is balanced.
 
You are correct we can't know what loads will be applied to what sockets but for sure feeding that many spurs into one point on the ring makes heavy loads on those spurs more likely to unbalance the ring. Therefore the design isn't suitable for ensuring a normal distribution of usage would create a balanced load.

That's my view on looking at the diagram and my interpretation of the regs based on it.
 
Get used to it. Every trade and profession has its own specific lingo. Just ask or Google if you don't know.

Here's a few for you to look up before the next lesson. Hint: there's a list of abbreviations in the BYB.
DNO, ELV, SELV, RCBO, RCCB, FCU, BC, CPC, DB, GLS, IR, MFT, PIR, RFC, SES, SWA, UKPN

I'll have a stab at them without looking in the BYB.

DNO = Distribution Network something
ELV = Extra low voltage
SELV = Safety extra low voltage
RCBO = Residual current breaker with overcurrent
RCCB = dont know but same as RCD
FCU = Fused connection unit
BC =
CPC = Circuit procetive conductor
BD = Distribution board
GLS =
IR = Infra red
MFT =
PIR = don't know motion sensor thing
RFC =
SES =
SWA = don't know armoured cable
UKPN
 
Because the junction box you have shown will not take all the cables (max of 4) you show 5

Good observation, however I believe you can push two 2.5mm2 cables into the push terminal, it says so in the lid of the connection box
 
You are correct we can't know what loads will be applied to what sockets but for sure feeding that many spurs into one point on the ring makes heavy loads on those spurs more likely to unbalance the ring. Therefore the design isn't suitable for ensuring a normal distribution of usage would create a balanced load.

That's my view on looking at the diagram and my interpretation of the regs based on it.

Thank you for your view, it is a view I share, but if you had an appliance that drew allot of current on the last socket, would that design then be acceptable?
 
What last socket? You have a ring so no end as such and spurs? But in a normal ring (RFC Ring Final Circuit) any heavy load anywhere on the ring has the benefit of its supply coming both directions down the ring.
Tapping a lot of spurs from one point of the ring is concentrating loading on the ring to that point. A single double socket could draw 26A max from that point on the ring. Each spur can take up to 26A so with 2 you have 52A 3 65A 4 104A
The ring will be protected by an overload device but we don't know what that is and what its characteristics will be but its possible we could be drawing a lot of current via that one junction box.
 
What last socket? You have a ring so no end as such and spurs? But in a normal ring (RFC Ring Final Circuit) any heavy load anywhere on the ring has the benefit of its supply coming both directions down the ring.
Tapping a lot of spurs from one point of the ring is concentrating loading on the ring to that point. A single double socket could draw 26A max from that point on the ring. Each spur can take up to 26A so with 2 you have 52A 3 65A 4 104A
The ring will be protected by an overload device but we don't know what that is and what its characteristics will be but its possible we could be drawing a lot of current via that one junction box.

The junction box is rated at 30A, you cant pull more than 32A through the circuit for any length of time anyway. Each double socket can pull 26A and you can have an unlimited amount of sockets so adding up the limits that can be pulled is not really relevant when considering the design of a RFC. The socket marked red in the picture is the one I was referring to as the last socket. Each spur can pull 26A, 13A each single socket and 2.5mm2 cable in certain conditions is rated at 26A, so there is no problem there. The JB pulls current from the left cable and the right cable a total of 52A, can be supplied.

You could be right I guess, is it only that the junction box is the weak point? What if you have a junction box rated at a higher ampage?
 
I'll have a stab at them without looking in the BYB.

DNO = Distribution Network something
...
SWA = don't know armoured cable
UKPN
Not bad. But worth looking them up. It's easy to guess at something that's nearly right, but not quite.
 

Reply to Spur from Ring Final Circuit in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi everyone, I've got an electrical ring circuit that looks somewhat like the drawing below, where the blue sockets are part of the main ring and...
Replies
2
Views
1K
I read that it is against the regs that a ring final circuit cannot be just a ring with with spurs off it. In short, a ring must have sockets on...
Replies
86
Views
6K
Ok. Can you cut a ring in half, add junction box, then run a spur off it? I thought it had to be from a socket? Mate of mine wanted me to see if...
Replies
3
Views
714
For some Strange reason we have three Circuits running in the Kitchen i think for two OLD Cookers and a Ring Circuit for the house. Well the...
Replies
18
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock