Discuss Spur from Ring Final Circuit in the DIY Electrical Advice area at ElectriciansForums.net

I'd lookup the actual current over protection devices will trip at. You can take more than 32 A from a 32A protection device and that varies on the device.
BS7671 does state that there maybe ways to achieve the requirements and if you think you can argue thst case then alls fine.
 
I'd lookup the actual current over protection devices will trip at. You can take more than 32 A from a 32A protection device and that varies on the device.
BS7671 does state that there maybe ways to achieve the requirements and if you think you can argue thst case then alls fine.

You can take more than 32A from a 32A MCB for a limited amount of time, until the bimetallic strip in the device gets hot enough and bends far enough to trip it. It will eventually trip if you pull more than 32A on all BS rated devices.

I believe the chart you may be thinking of is the one that shows how much current is needed in a short circuit fault situation to trip the device in 0.4 seconds, That will activate a solenoid and instantly trip the MCB
 
Last edited:
Gigsy can you stick to one thread please it just causes confusion
Decide which one you want and the other one can get deleted
 
Gigsy can you stick to one thread please it just causes confusion
Decide which one you want and the other one can get deleted
?

They are two threads, two different topics. One about ring final spurs and one about J803 junction boxes. I don't mind if you delete both threads, Everyone has been most helpful and have answered my questions. Thank you everyone :)
 
They are push fit connectors with cable grips, so evidently yes they are in a suitable maintenance free box!!

Have you never heard of a J803?
Yes I have, but you didn't mention that on your 1st post if I recall corectly
 
The other one is Gone. You say they are 2 different threads but this one was enough, you started talking about h803's then started another thread about the same thing which then had members answering the same questions over 2 threads.
 
I assume that you are adding 3 extra sockets to the circuit,why don't you install them on the ring.Even how well installed I would try to avoid using j.b's even MF ones under floors.
 
I assume that you are adding 3 extra sockets to the circuit,why don't you install them on the ring.Even how well installed I would try to avoid using j.b's even MF ones under floors.

Thank you, I managed to wire a ring by pulling through some cables, it was hard but I did it in the end, Ended up with just one spu, had to use a junction box cos could not pull the cable through
 
What a preposterous comment to make!
If you need to ask then I'd (respectfully) suggest you shouldn't be doing electrical work. The suggestion that an EIC or MWIC is dictated by Building Regs is wrong. The two are separate entities. If you do an alteration, addition or new installation you complete the appropriate certificate. Building notification is a separate issue.
 
If you need to ask then I'd (respectfully) suggest you shouldn't be doing electrical work. The suggestion that an EIC or MWIC is dictated by Building Regs is wrong. The two are separate entities. If you do an alteration, addition or new installation you complete the appropriate certificate. Building notification is a separate issue.

You don't have a clue m8, I am talking about the law. If you alter or add to a circuit there is no stipulation in law that you have to test the circuit, end of!
 
You don't have a clue m8, I am talking about the law. If you alter or add to a circuit there is no stipulation in law that you have to test the circuit, end of!
You're the cable chased across the ceiling bod.
 
@Gigsy Can you please give the trusted members a bit of respect please , they have earned it by helping people like you in the past. It doesn't sit well when you join a forum to ask for help from people with more knowledge than you and then choose not to accept it. You have already been given a warning point in this thread by a member of staff, which isn't great considering you only joined 12 days ago.
Just food for thought!!
 
You don't have a clue m8, I am talking about the law. If you alter or add to a circuit there is no stipulation in law that you have to test the circuit, end of!
What Law are you talking of Gigsy?
 
He can't answer you Pete, he's just been banned.
 

Reply to Spur from Ring Final Circuit in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi everyone, I've got an electrical ring circuit that looks somewhat like the drawing below, where the blue sockets are part of the main ring and...
Replies
2
Views
1K
I read that it is against the regs that a ring final circuit cannot be just a ring with with spurs off it. In short, a ring must have sockets on...
Replies
86
Views
6K
Ok. Can you cut a ring in half, add junction box, then run a spur off it? I thought it had to be from a socket? Mate of mine wanted me to see if...
Replies
3
Views
714
For some Strange reason we have three Circuits running in the Kitchen i think for two OLD Cookers and a Ring Circuit for the house. Well the...
Replies
18
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock