Discuss spurs in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
4
what is maximum amount of spur sockets taken from a main , the main amperage can be changed easily the wiring is 2.5 and a ring main is not possible without a lot of work as this is a large old house which has been wired this way , there will only be one large consumer a water heater .
 
you can take only 1 outlet as a spur from a ring final unless you fit a 13A FCU
 
what is maximum amount of spur sockets taken from a main , the main amperage can be changed easily the wiring is 2.5 and a ring main is not possible without a lot of work as this is a large old house which has been wired this way , there will only be one large consumer a water heater .
1 spur per socket on the RFC See Appendix 15 BS 7671
 
what he said about what he above said ^^^^^. although 4mm is capable of handling the current in itself, adding several outlets to the same point on the rfc could overload the 2.5mm rfc cable especially if the point was close to one end of the rfc.
 
If you have a ring final circuit then the recommendation is that the number of unfused spurs does not exceed the number of point on the ring. e.g. with ten sockets of the ring a maximum of 10 unfused spurs is recommended. The number of fused spurs is unlimited.
An unfused spur will only supply a single point of use.
In practice you would be looking at the ring loading and ensuring that there were not a concentration of current drawn at one point of the ring.
 
If you have a ring final circuit then the recommendation is that the number of unfused spurs does not exceed the number of point on the ring. e.g. with ten sockets of the ring a maximum of 10 unfused spurs is recommended. The number of fused spurs is unlimited.

I'm clearly missing something here, as both you and Pete999 have mentioned this. I can't find anything in the current edition of the regs about a limit on number of spurs, although maybe I've read it in a previous edition.
 
I'm clearly missing something here, as both you and Pete999 have mentioned this. I can't find anything in the current edition of the regs about a limit on number of spurs, although maybe I've read it in a previous edition.
Have you looked at Appendix 15 in the BYB
 
Having re-read the OP, I'm not sure we're talking about a ring....

"what is maximum amount of spur sockets taken from a main , the main amperage can be changed easily the wiring is 2.5 and a ring main is not possible without a lot of work as this is a large old house which has been wired this way"

I think he's talking radial.
 

Reply to spurs in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

This question has probably been asked several time but things change. The house I'm living in now was built in the 1960's and has a ring main...
Replies
15
Views
863
Hi Guys, Long time member and not a regular user here. I do pop in here when the odd unknown pop's up and unable to locate an electrical dilemma...
Replies
4
Views
849
Ok. Can you cut a ring in half, add junction box, then run a spur off it? I thought it had to be from a socket? Mate of mine wanted me to see if...
Replies
3
Views
741
Grateful if someone could offer some advise, I'm struggling to find a definitive answer to this. I have a double socket, it was on the ring main...
Replies
8
Views
634
We have a room in the house that was the kitchen. That has been relocated to a different area, so the old kitchen has been sold off and the room...
Replies
2
Views
610

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock