4kw mate. Only a baby.Out of interest, what size is the pump motor?
Nice one. Makes sense re the star connection. What If its to be in delta?Refer to the manufacturers instructions re: connecting in star or delta, and with a multimeter set to resistance ascertain the winding pairs e.g. U1/U2, V1/V2 and W1/W2, (the earth should be the easiest to determine) If to be connected in star formation then connect U2, V2 and W2 together and use the remaining for the supply L1/U1, L2/V1 and L3/W1.
Brilliant. If ever in Kent I owe ya a beer! Cheers mate.In delta you would still need to find the start and finish of the windings as stated previously but connect U1/W2 together, U2/V1 together and V2/W1 togther with L1, L2 and L3 respectively. Be mindful of machine rotation for both cases.
Haha cheers. Sorry just one more thought. If the motor has tails for star delta connection and I'm wiring it DOL, how would I decide if it's star DOL or delta DOL? I mean it's 4kw so I'd assume delta but will the motor plate say?Oh, and welcome to the forum!
Daft question but why would anyone want to run it in Star then? Why would you choose to run it at a reduced torque?Assuming it is rated 400V when connected in delta then it will run at reduced torque if connected in star.
That's ace mate thank you.I suspect the motor should be run in delta, assuming it is rated at 400V in delta then to run it in star and achieve the same torque you would need a 690V supply. If the motor has a cooling fan to draw air across the casing fins then it may not be cooled sufficiently if connected in star using 400V which could result in winding burn out. There could be many reasons why it has a 7 core flying lead from it, assuming one is the cpc.
No such thing as a Star Delta Motor Tom, it's how it is connected that determines wether it is S/D, can you post a picture of the wiring in the starter?Hello everyone. I have a new star delta pump (7 core flying lead) that has to be made off into a DOL single contactor starter. Is this possible and does anyone know how?
No such thing as a Star Delta Motor Tom, it's how it is connected that determines wether it is S/D, can you post a picture of the wiring in the starter?
No such thing as a Star Delta Motor Tom, it's how it is connected that determines wether it is S/D, can you post a picture of the wiring in the starter?
I am not sure I will check it when I go to see it. Iv been sent a pic of the dol though...Out of interest, what size is the pump motor?