Discuss Static caravan in the Industrial Electricians' Talk area at ElectriciansForums.net

c.boy

-
Reaction score
0
Hi all,
Got a look at a job today in a traveling site, we are installing a supply to a static caravan! The supply is tncs to a metal clad d/b in an out house,all circuits have rcbo protection!! There is a 100a rcd fitted,fed from the main isolator switch then feeding the d/b!! My ? is obviously the ze was very poor and this was put in at some point to overcome that, however with all circuits now protected by rcbos is the rcd still required?? Tight for space to install 4x4 box for the s.w.a supplying the van post.And forgive me if I'm being thick but how does fitting and rcd solve the high ze??

An an earth rod will be installed for the caravan supply tho!!
 
because a TT system will have a Ze value too high to trip a fuse/breaker in the event of a fault, a RCD will perform this function with a Zs of up to 1667 ohms for a 30mA device.
 
what does the existing RCD protect? is it there to protect the feeder cable to the DB?
 
Hi all,
Got a look at a job today in a traveling site, we are installing a supply to a static caravan! The supply is tncs to a metal clad d/b in an out house,all circuits have rcbo protection!! There is a 100a rcd fitted,fed from the main isolator switch then feeding the d/b!! My ? is obviously the ze was very poor and this was put in at some point to overcome that, however with all circuits now protected by rcbos is the rcd still required?? Tight for space to install 4x4 box for the s.w.a supplying the van post.And forgive me if I'm being thick but how does fitting and rcd solve the high ze??

An an earth rod will be installed for the caravan supply tho!!
The caravan supply needs to be a 30 ma double pole RCD as you have converted the supply to a TT system.
 
The caravan supply needs to be a 30 ma double pole RCD as you have converted the supply to a TT system.
The supply hasn't been changed yet that's my ? The 100a rcd is splitting the tails from the isolator then to the 100a main switch on a consumer unit with all circuits on an rcbo.
 
Had another look today was late last night and head was fried!! I think you must have miss read my original post tho!! I've kept the out house on the tncs supply and the caravan on tt!!! I said the caravan was being put on tt not the out house!! Which had the 100a rcd feeding the rcbo fuse board!! Was a strange setup should have posted a pic thanks tho.
 

Reply to Static caravan in the Industrial Electricians' Talk area at ElectriciansForums.net

Similar Threads

Need some advice, I have 7 static caravans to connect which need to be connected via TT 1. All the vans have a 30ma RCD main switch internally...
Replies
6
Views
858
Hope this all makes as much sense as i can make of it and my "problem" can get sorted via some guru on here... Just a quick background on myself...
Replies
4
Views
936
Hi all, Grateful for your expertise regarding my confusion on the below. Context: French rural domestic property Single phase supply, TT...
Replies
12
Views
2K
Hi there , Currently doing a college project where i need to select protective devices for the contract. I'm now at the point of selecting SPDs...
Replies
5
Views
2K
Hi guys I was recently ask by a customer if/how his house could be supplied by his electric car. He wants to charge the car at night on low rate...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock