Discuss Strange fault - larger cable tripps mcb ????? Why ??? in the UK Electrical Forum area at ElectriciansForums.net

D

djjeff99

Hi There
I have a very strange one here , that no one iv asked seems to know the answer to .

On a recent test i found a 6mm XPLE SWA cabel protected by a 63A D rated mcb , for 3 phase motor circuit .
I desided to derate the mcb to a 50A but it triipped when ther motor was running .
So i then desided to upgrade the cable to a 10mm SWA to take the 63A mcb rating .
BUT IT TRIPPED !!
Strange thing is the 63 A MCB tripps when using the 10mm cable , but not when using the 6mm cable ????
I have even tried a different brand/length of cable and the same happens .
Everyone in the game i ask has never come accross this happening before , so i thought id give it a try on here ? :dizzy2:

Thanks
Jeff
 
the lower resistance of the 10mm may be allowing a higher start up current to flow.
 
should it not be the o/l unit on the starter that trips first for overcurrent, not the mcb? Have you ensured any of the integrity of the terminal studs/cable (or whatever) has not been damaged/inside the motor connection box. The motor could just be on its way out with an insulation fault? Looking at possible reasons for mcb tripping...
 
I will put the amp clamp on to see what exactly its pulling on start up , and i dont think it has a starter on it , but maybe it needs one .
 
Last edited by a moderator:
Also, check whether it is wired as star or delta configuration so you can read the correct rating off the motor plate, then set your o/l to this.
I would do a full insulation/resistance test on the motor before anything else tbh. Tripping an mcb with a much higher rating than the motor sounds more like a fault than overload if you are using a D type. As suggested, if it meggers out ok, stick a clamp meter on each phase as it could even be unbalanced.
 
A lot of shots in the dark here.... the first question is what size Kw is the motor and is it a star/delta motor?, how is it connected if its as suggested 'Direct on Line', what is the length of cable run to the motor and installation method.
Answer these questions and im pretty sure i can tell you why and what and how to solve it.
Mcb tripping etc means nothing and dosn't imply faulty motor until you know what size Mcb should be covering this motor so first thing first before everyone confuses you with random ideas..... What size is the motor and what is it doing as a workload.
 
Last edited:
A fan or pump is different to start than say a conveyor. Sorry I should have said load.
Soz Tony, i was mislead as you already pointed out what id posted which included the motor workload, so assumed you didnt mean that by the way you worded it as been a point not yet mentioned but hey ho'!, Same old - same old; OP disappears as soon as the right questions are asked lol
 
The company I worked for several years ago employed a firm of electricians to help us on-site guys install and connect up several new pieces of equipment as time was of the essence. A few bits of kit had no control cabinets at all so we had to design and build from scratch. We were amazed to find that none of the electricians had ever heard of a star/delta starter, let alone ELV control circuits. A few hours later they had been briefed in the art of reading a basic circuit diagram and the properties of contactors. As far as management was concerned we were all electricians so where was the problem....
 
i had this argument with someone who is supposedly a time served industrial electrician who could not read a drawing to wire up a very basic roller shutter motor starter

i was a 1st year apprenice at the time and did the job whilest my boss was sleeping off a hangover in the van
 

Reply to Strange fault - larger cable tripps mcb ????? Why ??? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, So I’ve been having a strange fault in my house which has just appeared over the past few days. About a month ago I moved my pc set up...
Replies
136
Views
14K
When putting in some duct for fibre broadband we also put in a few lengths of 63/50mm twinwall duct "just in case" we needed that, as we knew of a...
Replies
9
Views
1K
I've installed a garage consumer unit sub-main to an outbuilding in 16mm 3 core armoured, the insulation tests all come back fine - +800Mohms on a...
Replies
6
Views
2K
Doing an EICR on a top floor flat recently and run into an issue I often do - which is judging imperial sizes when they are larger than the...
Replies
22
Views
3K
During the time of phase absence measurement temporary earth fault was detected on the enclosure of 3 phase motor starter. I assume earth fault...
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock