Okay, I've got a pretty unusual problem that I've had over the last couple of days and I'd welcome some advice on this.

Currently we are carrying out electrical works on barn conversions into single and two bed homes. Fairly small, single storey.

Carried out second fix - sockets, lights (with lamps removed) etc. No current drawing equipment at all.

I started testing on Friday afternoon and did a global insulation resistance test which gave a figure of 5M ohm. Obviously I investigated further and found odd figures on different circuits:

280M ohm on one of the ring mains approximately. The figure fluctuates - not just rise, I mean rise and fall.
5M ohm on one of the lighting circuits.
300M ohm on the other lighting circuit.

The 5M ohm lighting circuit was isolated to the two bathrooms - one giving a reading of 5M ohm and the other giving a reading of 250.

Investigated the 5M ohm circuit which consisted of four unlamped spot lights and initially got odd readings on different sections. We found we could actually affect the readings by moving the cables around. Now we seem to be getting a reading of 500 rising to 1000+. Cables feel free, so not trapped.

This would be unusual enough but we are getting similar issues in four of the other units. We have a few circuits with very low readings - 5M ohms and a few with everything between 100 and 1000.

Checked readings with another testing and they corroborate the readings so it's not a tester issue.

Any thoughts?

I know that the figures are "acceptable" but surely this points to a problem that needs putting right.
 
Do you have any unused cable left which you can IR test? It would be unusual, but a batch of faulty cable would explain why the odd readings are present in multiple buildings.
 
We don't have any cable left from the original delivery, but we do have cable drums from further deliveries. They all test totally clear.

I have thought about faulty cable, and it still seems the most likely explanation to me, but we are getting faults on the 1.0mm and the 2.5mm. Not impossible, but surely this makes it far less likely to be the cause?
 
Have you checked the connections on your MFT? could be iffy connections
 
No, different leads.

Interesting Watson, well that knocks that theory on the head doesn't it? checked any connections on the actual installation, basic questions I know but when you can't find the answer it's usually staring you right in the face.
 
When you say insulation test are theses readings only between L & E ?

Is there any damp, i.e wet plaster, condensation...?

If moving the cable affects the readings then this would initially lead me to think there is a trapped cable / loose cable.
 
I'd also suspect high relative humidity/damp but it's summer in the UK so maybe unlikely. Are the cables in free air or in conduit, if in conduit maybe something soapy and moist was used as lubricant to assist with pulling.


**edit** I just read this post back to myself and I can only apologise for the last sentence, it didn't translate very well :)
 
Last edited:
Okay, I've got a pretty unusual problem that I've had over the last couple of days and I'd welcome some advice on this.

Currently we are carrying out electrical works on barn conversions into single and two bed homes. Fairly small, single storey.

Carried out second fix - sockets, lights (with lamps removed) etc. No current drawing equipment at all.

I started testing on Friday afternoon and did a global insulation resistance test which gave a figure of 5M ohm. Obviously I investigated further and found odd figures on different circuits:

280M ohm on one of the ring mains approximately. The figure fluctuates - not just rise, I mean rise and fall.
5M ohm on one of the lighting circuits.
300M ohm on the other lighting circuit.

The 5M ohm lighting circuit was isolated to the two bathrooms - one giving a reading of 5M ohm and the other giving a reading of 250.

Investigated the 5M ohm circuit which consisted of four unlamped spot lights and initially got odd readings on different sections. We found we could actually affect the readings by moving the cables around. Now we seem to be getting a reading of 500 rising to 1000+. Cables feel free, so not trapped.

This would be unusual enough but we are getting similar issues in four of the other units. We have a few circuits with very low readings - 5M ohms and a few with everything between 100 and 1000.

Checked readings with another testing and they corroborate the readings so it's not a tester issue.

Any thoughts?

I know that the figures are "acceptable" but surely this points to a problem that needs putting right.


Any hidden Junction Boxes? you said the readings fluctuated when you moved the cables, could be loose connections, just a thought.
 
Last edited:
barn conversions. could it be mice/rat/squirrel attacks on the cables?
 
Hi fellas.

No junction boxes nor mice attacks.

We actually isolated one of the faults to a bathroom lighting circuit. Just four spots from a switch, no leds. We seemed to be able to affect the reading by moving the cable.

The cable was free enough to pull a replacement cable through - which we did. Reconnected the new cable and the fault cleared. No sign of damage or moisture on the replaced cable - and it also now tests clear.

I've not come across anything like this before. The plaster is totally dry and has been for a couple of weeks now.
 
must be dodgy cable the. last year i had a 40m length of 3 core 6mm SWA where the brown (L) conductor went completely O/C within 2 weeks of installation. had to be dug up and replaced. as it was a gypsy site, no problem in getting grunts to dig up. lol.
 
.....The cable was free enough to pull a replacement cable through - which we did. Reconnected the new cable and the fault cleared. No sign of damage or moisture on the replaced cable - and it also now tests clear.....
Must have been some kind of containment ingress in the cable. Maybe the crate it arrived in fell off the dockside into the sea as it was being unloaded from the boat :)
 
Readings over the whole site seem to have improved slightly, although it is difficult to tell. I'm convinced that it isn't moisture - everywhere is so dry and most circuits are testing perfect.
 

Reply to Strange test results - advice requested in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi all, Testing question for you. I'm currently testing an existing domestic installation. The wiring is about 20-25 years old. We have rewired...
Replies
7
Views
1K
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K
Good day. First time poster. We recently had an electrician perform the EICR, as this is a newly purchased property I thought'd I would have the...
Replies
7
Views
674
We have had builders in, who have stopped for Xmas. My daughter tried to do a wash. The wash machine wouldnt. Its power socket is dead. I...
Replies
4
Views
624

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock