Discuss Stripping SWA - any quick methods in the UK Electrical Forum area at ElectriciansForums.net

gazdkw82

-
Arms
Reaction score
739
iv got a large amount of 4 core 10mm SWA to Weigh in.

Iv never took copper to a waste site before to get weighed in.

Few questions

Do they take the steel armouring too?
Is it actually worth stripping?
Has anyone used brownhills before?
Is there any quick ways to strip? It's took me ages to strip about 60 metres
 
4 core 10mm SWA to Weigh in

So, that weighs 998 grams per metre.

40mm² * 1000mm * density of copper per mm cubed = 358 grams per metre of copper

If you bin the steel, PVC and PE, you just threw away 64% of it's weight.

  • So, if the scrap dealer is only paying double for bright copper/kg vs the SWA/kg as is, you just lost money by stripping it.
  • If the dealer is paying 2.77 times, it's a tie, but you just wasted an awful lot of time/effort and now have a load of cr@p to get rid of.
  • If they are paying triple, you gained 8% by stripping it, but was it really worth all the effort and rubbish you've now got to dispose of?

The steel is practically worthless in that sort of quantity and not worth calculating.

Moral of the story - Don't bother stripping scrap cable!!!!!
 

So, that weighs 998 grams per metre.

40mm² * 1000mm * density of copper per mm cubed = 358 grams per metre of copper

If you bin the steel, PVC and PE, you just threw away 64% of it's weight.

  • So, if the scrap dealer is only paying double for bright copper/kg vs the SWA/kg as is, you just lost money by stripping it.
  • If the dealer is paying 2.77 times, it's a tie, but you just wasted an awful lot of time/effort and now have a load of cr@p to get rid of.
  • If they are paying triple, you gained 8% by stripping it, but was it really worth all the effort and rubbish you've now got to dispose of?

The steel is practically worthless in that sort of quantity and not worth calculating.

Moral of the story - Don't bother stripping scrap cable!!!!!

The scrap dealers around here pay around 40% of bright for PVC insulated and around 20% of bright for armoured.
 
around 20% of bright for armoured.

So five times the value for stripping it would be worth it, because you'll add 80% (5/2.77 in this case) value to what you already had. Still seems like a lot of effort though, depends on how quickly/efficiently you can strip it I guess.
 
Last edited:
Pete I have no use for it at the moment and I just don't have any room to store it
Can you not sell it as a going item? I mean 60M of 10mm4c must be worth more as an installation item, than spend hours scrapping it, I can understand the storage problems, but someone must have a use for that amount of cable. If you are that sure tou want to get rid of it, see how much a scrap dealer will give you as is.
 
good point pete. Ill look into that.

what about the 4C 25MM. I need that gone too and less likely someone is going to want that size cable
I would be surprised if ant scrap dealer didn't have an outlet for that amount of SWA, weigh together what they offer you as is, against the time and effort it going to take to strip it
 
So basically load the car up and take
It over there and see what they offer as is? Then ask what they would offer stripped?
Yes you could do that. you just have to justify the time and effort it would cost you in stripping the outer cover, the armour and the insulation to produce bright copper.
Advertise the cable in the for sale area you might be presently surprised, remember a lot of these scrap dealers send unstripped large cable to a third party for stripping,or a electrical contractor who might be interested, another thing to think about is the Police, that amount of SWA might ring a few bells, I'm not saying it's iffy cable, but you know how paranoid the Police are.
 

Reply to Stripping SWA - any quick methods in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I never did like transformer theory in my degree course and that was 40 years ago. I'm a boat builder now and we tend to have big battery banks...
Replies
3
Views
1K
Those week I have mostly been fitting 20 x 10W flood lights on the sloping edge of a converted mill ceiling, nothing is straight, nothing level...
Replies
3
Views
1K
Hi all, My first post here, thought I'd see if it was possible to get some advice or tips... Basically, I had a large amount of block paving and...
Replies
80
Views
12K
I need to augment the underground supply to remote workshops at my own house. I’m struggling to understand the practical implications of voltage...
Replies
11
Views
2K
Hello all, I've just been perusing the AM2/E/S threads on here. Thought you might like a bit of a review. If, like I did, you find yourself...
Replies
7
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock