Hi,
i have been to complete a condition report in a flat today and would appreciate a bit of advice.
The db was fed via a 16mm twin and earth sub main approx. 12m run, protected by the 6o amp main fuse, tncs system. Gas bonded in 10mm at main cutout, water bonded in 10mm at db.
Main earth at db is the 6mm in the twin and earth. Dual rcd db.
I have c2 the set up, but an electrician i work with is saying c3. Do you agree it is a c2.
I believe a c3 may apply if it was a tns system and the adiabatic equation was satisfied.
Also, to rectify this would running a separate 10mm earth from the cut out to the db be ok, giving a combined csa of 16mm, or would we have to run a separate 16mm earth to comply.
Just wondered what everyone's thoughts were on this?
All advice is appreciated.
Thanks
Craig