Discuss Summerhouse supply - thoughts? in the UK Electrical Forum area at ElectriciansForums.net

daveb

-
Reaction score
64
thoughts on this one folks....

6mm armoured cable to supply summerhouse. Wiska box screwed onto side of the house at a low level beside vents - this allows a pathway under floor to front door hatch where fuse board is.

Option 1 - terminate the armoured cable into the wiska box on side of house. Join with 6mm twin and earth inside box with crimps or terminals.

Option 2 - use the wiska box to feed the cable through under the floor. Join the cable nearer the hatch to allow crossover to twin and Earth.

Note 1 - wiksa box was added to outside wall for neatness. Rather than having an ugly hole with cable running through it.

Note 2 - want to avoid terminating the armour into the board for a few reasons (ease/ access/ space etc)
 
Really cant see the point in an external wiska box, just drill a neat hole and make good....cant be any 'uglier' than a black box. Cant you terminate the SWA outside of the DB in a galv through box or adaptable box?
 

Reply to Summerhouse supply - thoughts? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
So far I have never had to deal with a new supply but a possible site we are looking at will need some major changes and so I wondered if folks...
Replies
2
Views
696
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
709
Hi all, New to the forum. I have been asked to look at this for one of our guys who's had an issue onsite after some electrical works had been...
Replies
4
Views
712
Had a call from a local caravan site… under new ownership, and creating some new pitches. Went to site to have a chat, the guy already knew I’ve...
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock