You describe no overcurrent protection at the supply, this would be best before it goes through the wall as otherwise you are relying on the DNO supply fuse which will not be suitable for a 6mm² cable.
The cable is running through a wall so is not in free air, there is a significant limitation to the heat loss.
You have a total maximum load of 84A from the sum of circuit breakers, though this is not the design current.
You are reading the wrong table for the the cable type.

Overall, no, 6mm² cable is unsuitable for this application. Depending on your supply fuse size 16mm² or 25mm² cable would be more appropriate.

It is not fed direct from the DNO fuse , this feed come via a 63A RCD 30mA from the DNO fuse box ! .
Well being as its a grain store you have now got to be very carefull with ip rating of everything in that vasinity,may be worth reading DSEAR. So after everybody telling you NO its not ok to use 6mm cable youve used it anyway?? Why dont you post a pic of the incoming 3phase set up and maybe we can give more accurate advice.


No not 6mm2 , I am using 10mm2 as I have just stated ! .
 
You describe no overcurrent protection at the supply, this would be best before it goes through the wall as otherwise you are relying on the DNO supply fuse which will not be suitable for a 6mm² cable.
The cable is running through a wall so is not in free air, there is a significant limitation to the heat loss.
You have a total maximum load of 84A from the sum of circuit breakers, though this is not the design current.
You are reading the wrong table for the the cable type.

Overall, no, 6mm² cable is unsuitable for this application. Depending on your supply fuse size 16mm² or 25mm² cable would be more appropriate.

It is not fed direct from the DNO fuse , this feed come via a 63A RCD 30mA from the DNO fuse box ! .
Well being as its a grain store you have now got to be very carefull with ip rating of everything in that vasinity,may be worth reading DSEAR. So after everybody telling you NO its not ok to use 6mm cable youve used it anyway?? Why dont you post a pic of the incoming 3phase set up and maybe we can give more accurate advice.


No not 6mm2 , I am using 10mm2 as I have just stated ! .
 
The 63A 30mA RCD does not provide over current protection! You don't understand the basics...The thread should be closed before you burn the place down or kill some one.
 
Last edited:
Can you not post a picture of the setup, your explanation may be at odds with what is actually in place.
 
Also what is an 83A device? That's a new one on me!
 

Reply to Supply to a 63A RCB in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

Client currently has a DB in his outhouse. It feeds a pool pump and an air source heat pump. It is currently being supplied using a 4mm T&E cable...
Replies
9
Views
604
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
407
DIYer question. I have a 32 amp supply going from consumer unit in garage to kitchen. It supplies an induction hob only. The cable is easily...
Replies
34
Views
3K
Background: I am not an electrician, I am a retired professional engineer high power broadcast transmitter design , but am dabbling outside my...
Replies
15
Views
2K
I have a baffling problem with a newly-installed PIR floodlight and I'd like advice from the forum as to whether it's defective (and should be...
Replies
5
Views
487

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock