A customer has asked me to price a job for them so here is the scenario.

Old milking shed with a 10mm 3 core SWA supply that is to be converted to office/annex.

Client requires 2 x 16 amp socket circuits, 1 x immersion circuit and 1 x 6 amp lighting circuit.

SWA cable run is 15 M approx.

My calculations (if correct) say that the 10mm SWA will support a 50 amp supply and then applying diversity that the cable will support the demand of the above circuits, also I think but am not 100% sure that the 10mm cpc in the SWA will be adequate for bonding of oil and water supplies to the building (supply is tncs).

I would appreciate anyones views on this scenario.
 
A customer has asked me to price a job for them so here is the scenario.

Old milking shed with a 10mm 3 core SWA supply that is to be converted to office/annex.

Client requires 2 x 16 amp socket circuits, 1 x immersion circuit and 1 x 6 amp lighting circuit.

SWA cable run is 15 M approx.

My calculations (if correct) say that the 10mm SWA will support a 50 amp supply and then applying diversity that the cable will support the demand of the above circuits, also I think but am not 100% sure that the 10mm cpc in the SWA will be adequate for bonding of oil and water supplies to the building (supply is tncs).

I would appreciate anyones views on this scenario.

don't think extending the tncs earthing system with such a small armoured would be up to scratch.as an annex
sepearte 10mm required for oil and gas at mains position would of thought a 25mm SWA supply would be required or make the milk shed a TT system..
i would measure the Ze to see what your up against.
 
Last edited:

Reply to Supply to an outbuilding in the Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock