- Reaction score
- 6,530
Good pointIf it's not a cpc then it just requires supplementary bonding to earth
I'm just thinking during the masonry drill attack the armour may be called upon to act as cpc so beef it up ?
Discuss Swa bonding, what method. in the Electrical Forum area at ElectriciansForums.net
Good pointIf it's not a cpc then it just requires supplementary bonding to earth
Depends as the steel armour conductivity isn't the same as copper so tho you might use a fly lead of 10mm the armour may not be even that equivalentGood point
I'm just thinking during the masonry drill attack the armour may be called upon to act as cpc so beef it up ?
Reg 543.2.7 rather clouds all this.The banjos don't even need to be linked together if glanded into a bit of steel trunking that's earthed.
What is the jist of it without me getting off me couch and actually reading it?Reg 543.2.7 rather clouds all this.
Na that's if you use conduit say as the cpc and you take a fly lead from the metal back box to the socket as the conduit is the cpc.
Agreed.Depends as the steel armour conductivity isn't the same as copper so tho you might use a fly lead of 10mm the armour may not be even that equivalent
exactly my thoughts or using 2core SWA and the armour as the CPC.Na that's if you use conduit say as the cpc and you take a fly lead from the metal back box to the socket as the conduit is the cpc.
In this case the trunking is not acting as a cpc it mearly becomes an exposed conductive part because the swa is glanded to it.
People don't gland it to the board enclosure because they are too lazy to find a simple solution to do so, just leave it floating in the cavity no one will know is the remit these days.
Don't think it is correct at all but it is the nature of the trade now because people do not have skills to engineer solutions.Thing is, even if the armour isn't being earthed at both ends. It still needs glanding. It needs terminating correctly!
I'd sack any "electrician" who thought this was a solution.
An westwood, I'm not saying you think this is correct.
Of course it needs to be earthed.
As it's an exposed conductive part who actually said it needs bonding as in extraneous??
I said supplementary bonded to earth or ' earthing ' which is different to protective bonding ,as in extraneous parts
Don't think it is correct at all but it is the nature of the trade now because people do not have skills to engineer solutions.
Couldn't agree more Rob.It's not following the regs though, everything should be suitably terminated (or words to that effect).
Maybe it's just me, but there seems to have been a huge influx on a few forums all with similar questions. god knows whats going on.
Hi all
Just need your advice, theirs a discussion going on atm on site between a couple of sparks. We have around 50 apartments being fed by 3core swa from a panel room all glanded into the top of a run of trunking, armour isn't used as cpc. One spark is saying we need to run individual 16mm earth's to each gland
Another is saying 10mm to the first of each set and then looping. I would have thought just bonding the trunking near the board adding some bonding tags in-between the trunking sections and bolting the banjos on would suffice. Tbf the trunking is <o.o1 atm anyway to met. So what's your opinion and regs if possible, don't have book with me.
Thank you.
Personally I would use Piranaha nuts (think they do a 32mm size) on each SWA and verifiy that the trunking is solidlybondedearthed. No need for daisy chain links IMHO. What size are the subs?
Reply to Swa bonding, what method. in the Electrical Forum area at ElectriciansForums.net
We get it, advertisements are annoying!
Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.