This.

And I think it's nuts saying it does not require it. And I just don't care if it's written in a book or not.

If that cable gets damaged that braid is likely to become live.
I am not saying yes or no to earthing it, merely where is the guidance. How are you judging its fault current carrying capabilities.
 
I am not saying yes or no to earthing it, merely where is the guidance. How are you judging its fault current carrying capabilities.

I don't think anyone is using the braided screen as an earth cpc. They are just earthing the screen as its a sensible thing to do.
 
I don't think anyone is using the braided screen as an earth cpc. They are just earthing the screen as its a sensible thing to do.
I never suggested this, my point being if it is required to carry fault current due to cable damage where is the maths to assess its fault current carrying capabilities.
 
I never suggested this, my point being if it is required to carry fault current due to cable damage where is the maths to assess its fault current carrying capabilities.

It would only need to be assessed for fault current carrying capability if used as a cpc surely ?
When earthed it is connected to cpcs whose capability for fault conditions has already been assessed and verified.
 
I never suggested this, my point being if it is required to carry fault current due to cable damage where is the maths to assess its fault current carrying capabilities.

Sorry mate. I miss read your post.
I haven't seen anything for the fault current carrying capabilities of the screen.
 
Hi - found this briefing note from BASEC, the official British Approval Service for Electric Cables (I think). They explain a bit more about the status of SY ++ .

Their last para is stark : "We therefore urge extreme caution in accepting the use of YY and SY cable types for UK fixed installations, and to contact the BCA on 0208 946 6978 ..."

BASEC - British Approvals Service for Cables - http://www.basec.org.uk/frontend/custom/print.cfm?part1=News&part2=Basec-News&part3=Be-Cautious-of-Midleading-Claims-Associated-with-YY-and-SY-cables&print=1
 
Their last para is stark : "We therefore urge extreme caution in accepting the use of YY and SY cable types for UK fixed installations, and to contact the BCA on 0208 946 6978 ..."

What is classed as "fixed installations"?
I did see something on a NICEIC site stating a fixed installation is something that “would stay if the business moved.”
 
I never suggested this, my point being if it is required to carry fault current due to cable damage where is the maths to assess its fault current carrying capabilities.

Do you asses this when earthing cable basket?

No, so I don't see the relevance of its ccc especially as it's not a cpc.
 
We used to use this cable a lot in commercial situations for computor installations, the electrical consultants required the braid to be earthed at the distribution board end, because a capacitance can build up in the braid if not earthed down. And if more than one socket on a circuit the braid would be continued through to the last socket on the run.The braid was peeled back, sleeved with g/y and then lugged off and grounded at the distribution point, also large plastic stuffing glands were used for entry to enclosures.
 
It would only need to be assessed for fault current carrying capability if used as a cpc surely ?
When earthed it is connected to cpcs whose capability for fault conditions has already been assessed and verified.
People are quoting it should be earthed in case the cable gets damaged, say by a nail. What happens when the nail causes a short between a line conductor and the braid, fault current flows. So my point is can the braid carry the fault current and sufficient current without any deterioration of the braid to cause disconnection of the circuit. I am not suggesting its use as a cpc, but if it is earthed there is a possibility it may carry current under fault conditions.
 
I understand what you are saying @westward, and this is the very point I have been trying to make, if you wish to use SY then because it falls outside the BS7671 then its down to the installer to confirm if the braiding will be adequate to carry a fault current, the stuff I have used in the past has met this criteria as I have sourced the manufacturing info myself but I cannot say this is the same for every piece of SY out there, but I would say its best to earth than not to, given that even if it does take damage under a L/E fault then it should still trip the OCPD and investigation to why the circuit tripped should see it taken out of service anyway.
 
My take is that if the braid is an exposed conductive part then it will need earthing.
I suppose you could trim the braid and tape it so that it's not accessible when the circuit is live, then say it's not an exposed conductive part so doesn't require earthing. I don't know why anyone would do that, just earth it and be done with it.
 
I understand what you are saying @westward, and this is the very point I have been trying to make, if you wish to use SY then because it falls outside the BS7671 then its down to the installer to confirm if the braiding will be adequate to carry a fault current, the stuff I have used in the past has met this criteria as I have sourced the manufacturing info myself but I cannot say this is the same for every piece of SY out there, but I would say its best to earth than not to, given that even if it does take damage under a L/E fault then it should still trip the OCPD and investigation to why the circuit tripped should see it taken out of service anyway.
Yeah I know you get the drift, interesting you find it acceptable the braid may suffer damage under fault conditions, this is not acceptable and is the point I am trying to make.
 
Yeah I know you get the drift, interesting you find it acceptable the braid may suffer damage under fault conditions, this is not acceptable and is the point I am trying to make.
It's not really the point whether the braid will suffer damage, but that without earthing it a fault such as a nail penetrating the braid and live conductor will be live.
Not only that but the braid will be live along the whole length of the installation.
 
It's not really the point whether the braid will suffer damage, but that without earthing it a fault such as a nail penetrating the braid and live conductor will be live.
Not only that but the braid will be live along the whole length of the installation.
Isn't it, the braid should maintain it's integrity under fault conditions so the circuit disconnects whether the cable is no longer serviceable or not. It seems to be the case for all other circuit configuration unless SY is involved, just earth it job done no thought required.
 
Isn't it, the braid should maintain it's integrity under fault conditions so the circuit disconnects whether the cable is no longer serviceable or not. It seems to be the case for all other circuit configuration unless SY is involved, just earth it job done no thought required.

Defiantly not. If the braid is an exposed conductive part then it will need to satisfy the regs regarding disconnection time if a fault occurs. This may be earthing it, it may require an rcd. If you can't guarantee the disconnection time then it should not be used.
So you see, lots of thought.
Just ignoring it because you're not sure that it can maintain it's integrity under fault condition would come under the heading 'no thought required'
 
Defiantly not. If the braid is an exposed conductive part then it will need to satisfy the regs regarding disconnection time if a fault occurs. This may be earthing it, it may require an rcd. If you can't guarantee the disconnection time then it should not be used.
So you see, lots of thought.
Just ignoring it because you're not sure that it can maintain it's integrity under fault condition would come under the heading 'no thought required'
Whether it is an exposed conductive part is debatable. As a matter of interest how are you assessing the braids ability to carry fault current whilst suffering no thermal stress.
 

Reply to Sy cable question in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Been asked to move, remove and add some sockets the kitchen and I’ll need to add a circuit for an electric hob. Looked at the board and it’s one...
Replies
17
Views
602
Hi. Im looking for some advice when calculating submain cables. Basically there is a new connection of 80Amps that is to be used for a dwelling...
Replies
5
Views
342
Background: I am not an electrician, I am a retired professional engineer high power broadcast transmitter design , but am dabbling outside my...
Replies
15
Views
2K
5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Replies
2
Views
491
Morning all So the site I'm based at recently had some work done (think partitioners). This package of work included electrical. This was...
Replies
44
Views
8K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock