Discuss testing dc cables in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Reaction score
6
well that was fun!
very limited testing of dc
turned up at job this morning a field of solar panels to test
5 mins instructions off we went
carried out irpos to earth array
neg to earth array
polarity
isc with test isolat
voc
managed to test 1 string pair on 50 invertors
not bad for first day!
 
question - when you say you tested them, do you mean you put the tester on and wrote down the results, or did you also double check that the results made sense in terms of what you'd expect for that many panels on a string in that level of irradiance / temperature?

or was someone else doing that last bit?
 
yes put tester on and wrote down results, irradiance is being carried out at later time as only 1 meter, each string had its own sheet to fill in results,he needed 25% of each inverter string tested as had a deadline to meet as connecting up tom.
there are 250+ invertors with 4 pairs each and this is just phase 1
learned quite a bit,just been thrown into it really as guy was crying out for help
everything goes back to the guys running it to check results but generally we were looking for reverse polarity, poor ir readings etc
also had to make off sunclick connectors(maybe wrong name)
 

Reply to testing dc cables in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

Morning guys! Went to look at a consumer unit change today with a PME supply. Now, right next to this was an old BS3036 60A fused mem cutout...
Replies
2
Views
648
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
405
Hello all, I've just been perusing the AM2/E/S threads on here. Thought you might like a bit of a review. If, like I did, you find yourself...
Replies
7
Views
2K
Hi guys, I am new to the forum so be nice! I used to install solar PV systems back when the tariffs were still good, and I've never had to go...
Replies
5
Views
5K
I know how I was taught to test a RCD, 6 tests in all two no go, two under 300 mS and 2 under 40 mS with no load. But thinking about it not so...
Replies
7
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock