There is an awful lot of waffle and nonsense in this thread. To dispose of Hightower's comment first, when the OP mentioned linking N & E at the 'bar' he presumably did not mean the N terminal bar DOWNSTREAM of the RCD. Of course that won't work! As people keep saying, If there is any kind of external earth present any load on the system will tend to split between N (passing through the RCD) and E (missing the RCD) and cause a trip - just like an N-E fault in a final circuit that causes a trip when a heavy load elsewhere in the house is switched on. And an L-E fault wouldn't trip the RCD, as Hightower says.
But this is beside the point for the OP - he hasn't got an E to work with. He wants to make his E bar 'E' solely by connecting it to N UPSTREAM of the RCD, i.e create a TN-C system, which is a no-go. The reason it's OK here is that it is done as part of the DNO works if, and only if, the N conductor meets the necessary criteria for TN-C-S. If it is not earthed at sufficient points, or is resistance is too high, or other connected installations are not compatible, then it cannot be used as TN-C-S, not least because of the risk of ALL THE EXPOSED METALWORK BECOMING LIVE IF THE N CONDUCTOR FAILS! How could you possibly be confident that the supplier's cable meets all the necessary criteria? Have you tested it all the way back to the substation and inspected all their earth rods?
Nope, TT earthing might never achieve stellar Ze figures, but at least it's better than seemingly low Ze 'earthing' that suddenly turns live on you when a badly made splice somewhere up a pole gives out.