Hi all, I would like to put a second earthing rod at a garage that is a little remote from the house, so as well a using the house earthing the garage would have the second rod, this would also add a second earthing route for the house, Is this permissible and can anyone see any problems occurring . Sidey
 
Hi Richard, Thanks for your reply, I had done the relevant impedance calculations and could see no problems but needed a second view in case I had forgotten something. If you have already had this reply it's because I'm just getting to grips with this site. Sidney
 
In principle it sounds fine to me subject to a few considerations.
1 the earth conductor connecting this second rod back the the main installations MET should be at least 6mm copper if my memory is correct and assuming it is not buried and is protected from mechanical damage etc etc.
2 the new earth rod should ideally be spaced from the existing rod by a horizontal distance equal to or greater than the sum of the lengths of both the existing and new rod.
The reason for this is that rods placed too close together will have overlapping spheres of influence, so under fault conditions will not achieve their best possible resist ace to earth.
But how on earth you will know the length of the existing rod I don't know! Even if the details of the original rod are recorded in the paperwork it will probably have been lost or eaten by the dog.
Apologies if this is teaching you to suck eggs, but it may be helpful to someone else reading the thread.




Sent from my iPad using Tapatalk
 

Reply to TT earthing system second rod in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi All, I own a country Villa out in the Spain countryside. Was having problems with water pressure so local tradesmen advised to get a water...
Replies
14
Views
968
Evening everyone . Currently looking at pricing a job up . It’s a hot tub supply . Outside socket with a few spare ways in an outdoor cu . 10mm...
Replies
7
Views
484
Afternoon all I am looking for some advice as on what to with the suppliers earth after a conversion to a TT system. Current issue is earthing...
Replies
10
Views
2K
5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Replies
2
Views
489
Hi all, There's 2 single fan ovens in the house my mother recently moved into. Posh elecronic AEG units. It's been sat empty for a year, so the...
Replies
19
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock