TT installation with two fuse boards as normal fitted with rcbo's.

First fuse board is fitted for the house installation and second fuse board is fitted for the shed with one 40A rcbo.

They had new tarmac put down which the owner said they damaged the cable going to shed.

The shed rcbo trips when they turn on the shower on the house installation board, but works when the shower is off.

Anyone seen similar fault before ??

I will go and test cable myself next time I'm down that way and try work it out
 
As Richards drawing explains at the common point ( the isco's in your case) of the neutrals the current splits according to the resistance of the fault vs the resistance of the circuit as resistors in parallel.
 
Last edited:
2 years ago I tracked a fault on a lighting / smoke circuit (on its own RCBO) - it tripped every time they switched on the oven (on a RCD).

Leakage from the oven to earth "pushed" the RCBO over the 23mA trip......

It does happen
 
How are the Cu's supplied? Tails into the house board and off the live side of main switch to second? or henley blocks? Or a circuit from house board supplying shed board???
 
If I change the rcbo to mcb of the armoured going to the shed and protect circuits at shed with rcd mains switch.

But then the armoured isn't protected for fault current as probably high ze reading

Which = replace cable with another route or rig up tarmac and repair if he knows where was damaged
 
N-E fault on the armoured going to shed, which is supplied from its own rcbo and separate enclosure which is fed from iscos

Il go have a good nosey if he willing to pay for it
 
If I change the rcbo to mcb of the armoured going to the shed and protect circuits at shed with rcd mains switch.

But then the armoured isn't protected for fault current as probably high ze reading

Which = replace cable with another route or rig up tarmac and repair if he knows where was damaged

Murray loop/wheatstone bridge.
 

Reply to TT installation in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Went back it a house after they upgraded shower to a 9.8kw, pulling 40a constant. We had wired it with 10sq and 40a RCBO. 10sq Neutral cable...
Replies
4
Views
986
Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Replies
6
Views
1K
Hi all. Sort of an interesting one. I had a call from a client to say she is getting a shock when using the shower. I told her not to use it and...
Replies
15
Views
1K
Hello all, Looking for help here as I've come across a strange call-out today. Bare with me here: Got a call from a customer saying they had...
Replies
13
Views
2K
I have a client with what appears to be an intermitent fault on the lighting, but trips the power. The installation has a 16th edition board with...
Replies
17
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock