- Reaction score
- 13
Hi,
Just a quick sanity check really around rcbo discrimination.. but also RCDs being used as L-E fault protection.
Scenario being a garage board change. Setup is: garage sub main fed from a main house CU. Initially wired in 10mm t&e with a 10mm earth along side it, run entirely in the ceiling of the house no walls etc., pops out on the external wall rear entry to a box, joints to a 10mm armoured that's running to the garage. Garage will have its own rod and small rcbo board
Given it's TT and realistically this is going to be reliant on the 30ma rcbo at the board to provide L-E protection am I right in thinking it has to be on a 30mA rcbo at the board (not that sourcing a 100mA rcbo would be particularly simple anyway, not to mention then running into discrimination issues with the 100mA unit before the main CU..), obviously having the 30mA RCBOs in the garage means no discrimination, but to me the discrimination issue is 'less bad' given the main CU is rcbos so you're not going to be taking out half the house with a garage fault, just potentially having to check both boards. Fault protection/safety taking priority over convenience here seems the sensible option to me..
Just a quick sanity check really around rcbo discrimination.. but also RCDs being used as L-E fault protection.
Scenario being a garage board change. Setup is: garage sub main fed from a main house CU. Initially wired in 10mm t&e with a 10mm earth along side it, run entirely in the ceiling of the house no walls etc., pops out on the external wall rear entry to a box, joints to a 10mm armoured that's running to the garage. Garage will have its own rod and small rcbo board
Given it's TT and realistically this is going to be reliant on the 30ma rcbo at the board to provide L-E protection am I right in thinking it has to be on a 30mA rcbo at the board (not that sourcing a 100mA rcbo would be particularly simple anyway, not to mention then running into discrimination issues with the 100mA unit before the main CU..), obviously having the 30mA RCBOs in the garage means no discrimination, but to me the discrimination issue is 'less bad' given the main CU is rcbos so you're not going to be taking out half the house with a garage fault, just potentially having to check both boards. Fault protection/safety taking priority over convenience here seems the sensible option to me..