- Reaction score
- 8,163
Morning all,
Did an EICR a couple of weeks ago and one of the things I commented on was the fact that the metal work of an undercounter fridge (the door hinge/skin mounting arrangements) did not have any continuity to the CPC of the circuit supplying it.
I can find no indication of it being a Class II appliance and this is backed up by the user manual I was able to find on-line which explicitly states the appliance should be earthed.
Today I'm doing the remedial work and obviously I'm going to need to investigate this lack of CPC continuity if it's 'a thing'
My sanity check question is am I correct in my assertion there should be continuity between the supply circuit CPC and the metal work that is accessible when the door is opened? I can find no reason in my head why that shouldn't be the case, but you guys may know otherwise.
Thanks
Did an EICR a couple of weeks ago and one of the things I commented on was the fact that the metal work of an undercounter fridge (the door hinge/skin mounting arrangements) did not have any continuity to the CPC of the circuit supplying it.
I can find no indication of it being a Class II appliance and this is backed up by the user manual I was able to find on-line which explicitly states the appliance should be earthed.
Today I'm doing the remedial work and obviously I'm going to need to investigate this lack of CPC continuity if it's 'a thing'
My sanity check question is am I correct in my assertion there should be continuity between the supply circuit CPC and the metal work that is accessible when the door is opened? I can find no reason in my head why that shouldn't be the case, but you guys may know otherwise.
Thanks