Discuss Up front Rcd question in the UK Electrical Forum area at ElectriciansForums.net

Okay this is becoming tiresome. Midwest, with the greatest of respect, you need to learn the difference between additional protection and fault protection.

Once you do, I assure you your lightbulb moment will come.
 
There is no need to be insulting. I'm just trying to understand how suggesting a 100mA RCD would provide protection against electric shock in the scenarios given?
 
There is no need to be insulting. I'm just trying to understand how suggesting a 100mA RCD would provide protection against electric shock in the scenarios given?
It won't is the short answer it's for fault protection only.
Or in the terms of a time delay discrimination as well
 
On the contrary, it is not my intention to insult you. I simply realised that until you understand the fundamental concept of fault protection, what I'm saying will be going over your head.

I have made no suggestion that a 100mA RCD will provide additional protection (BS 7671 definition) against electric shock, only that it will provide a form of back up fault protection.
 
Last edited:
You most certainly have.

May I suggest you read up on fault protection as once you do, what I'm saying will become a lot clearer.

(that's a genuine suggestion and not meant to be read in a patronising tone btw)
 
Before I go off and read up on fault protection;

So you weren't suggesting that using 100mA RCD would provide some measure of additional protection, in the event of the 30mA RCD failure?
 
No, I was suggesting that a 100mA s-type would provide a form of back up fault protection.

I stated that it would be an additional life saving safety measure rather than a substitution for one, but not that it would provide 'additional protection' as per the BS 7671 definition of 'additional protection'.
 
Last edited:
Oh well that's clarified that then. Still not quite sure about the 'additional life saving safety measure', but I supposed we've done that to death, if you pardon the pun.
 
Still not quite sure about the 'additional life saving safety measure'

By providing a back up form of fault protection should the sole means of fault protection which is prone to failure fail.

This is an additional safety measure that should the sole means of fault protection fail, would most likely be life saving.
 
I could debate some more as you are using terms which I think are opinion based 'additional safety measure', but as I said before, 'we've done that to death'. I'm sure you will like to have the last word though.
 
Additional safety measure
Optional safety upgrade
Improved safety device
Increased safety provision
Reduced danger implement
Best blimmin' practice

Take yer pick...

Whatever you wanna call it, the safety of the installation will be increased, a lot. Not really sure what's left to debate?
 
Additional safety measure
Optional safety upgrade
Improved safety device
Increased safety provision
Reduced danger implement
Best blimmin' practice

Take yer pick...

Whatever you wanna call it, the safety of the installation will be increased, a lot. Not really sure what's left to debate?

That's your opinion though, and as per definitions, opinions are always right. Getting the last word; it is the only proof of your argumentative success over competing editors :)
 
They make me nervous Ian, if that electrode connection corrodes or becomes detached that's it, they won't work. I'd always recommend their replacement ASAP, and how do you test one properly apart from the test button, nah best replaced IMO.
 
That's your opinion though, and as per definitions, opinions are always right. Getting the last word; it is the only proof of your argumentative success over competing editors :)

You can try all you like to write off my knowledge with "ah but that's only your opinion", or "you're only winning the argument because you just want to have the last word", but the fact remains that what I have said is objectively true. There is nothing subjective about it.

My argumentative success here is entirely based on the fact that I'm right, and you don't have a fundamental understanding of ADS.

Now go read up on fault protection.
 

Reply to Up front Rcd question in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
291
Hello! I've been racking my brain this evening about some RCD selections. I've been doing some work for a solar installer, and they've asked me...
Replies
5
Views
877
Hi Guys, Long time member and not a regular user here. I do pop in here when the odd unknown pop's up and unable to locate an electrical dilemma...
Replies
4
Views
835
Hi, I'm back in the electrical game after 9 years break so feeling a little rusty! I'm adding an additional socket to a circuit but the main RCD...
Replies
6
Views
1K
Hi all, Grateful for your expertise regarding my confusion on the below. Context: French rural domestic property Single phase supply, TT...
Replies
12
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock