I am in the process of pricing a DB change for a customer and am a little unsure as to what to do with the earthing conductor. The system is TT and the earthing conductor looks to be 6mm, tails are 16mm with a Ze of 47.7ohms. The main protective bonding conductors have already been upgraded to 10mm, as a stair lift has recently been installed and i assume it was done at this time by whoever carried out that work. The earthing conductor is not buried but where it is terminated to the rod it is protected against corrosion. And shows no signs of thermal damage. A quick look in the regs tells me that the minimum csa that would be allowed is 4mm. As i am bringing the DB upto current regs should i do the same dor the earthing or am i creating more work for myself and cost for my customer.
 
I am in the process of pricing a DB change for a customer and am a little unsure as to what to do with the earthing conductor. The system is TT and the earthing conductor looks to be 6mm, tails are 16mm with a Ze of 47.7ohms. The main protective bonding conductors have already been upgraded to 10mm, as a stair lift has recently been installed and i assume it was done at this time by whoever carried out that work. The earthing conductor is not buried but where it is terminated to the rod it is protected against corrosion. And shows no signs of thermal damage. A quick look in the regs tells me that the minimum csa that would be allowed is 4mm. As i am bringing the DB upto current regs should i do the same dor the earthing or am i creating more work for myself and cost for my customer.
If protected against corrosion and is mechanically protected you can go as low as 2.5mm in a TT so you may as well leave it.
 
Last edited:

Reply to Upgrading earthing conductor in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Evening Chaps As can be seen in the attached photo , the incoming supply cable has a Earth soldered to the outer sheath of the cable suggesting...
Replies
10
Views
1K
Hi All, I own a country Villa out in the Spain countryside. Was having problems with water pressure so local tradesmen advised to get a water...
Replies
14
Views
973
Hi there, Just a quick question. Does a main protective bonding conductor require UV protection when run outside? I am under the impression that...
Replies
3
Views
664
Evening all, Having a debate with a colleague about using the SWA armouring and a separate conductor both as CPC's for a circuit. So in theory...
Replies
7
Views
1K
Hi, I have always used banjos when earthing the armour on an SWA but have now switched to earthing nuts. I am making off a 10mm fly lead to the...
Replies
17
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock