Discuss Uploading Pictures (problems) in the Electricians Chat - Off Topic Chat area at ElectriciansForums.net

Welcome to ElectriciansForums.net - The American Electrical Advice Forum
Head straight to the main forums to chat by click here:   American Electrical Advice Forum

B

Barry White

Most pictutes I upload are hosted on photobucket but have in the past used the upload button but now it just asks for a url . Has something changed since the forum upgrade?
 
I will put it in staff room for you mate.
 
just trying it now and it seems to work cheers Richard edit it deffo works ,either its my altshiemers or its changed from the old forum layout.:(

Uploading Pictures (problems) Laundry - EletriciansForums.net
 

Reply to Uploading Pictures (problems) in the Electricians Chat - Off Topic Chat area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock