LlandrilloSpark

Fella's

I'm just writing up an EICR from last month, one of the findings was a lighting circuit on the non RCD side of the board where the cpc was used as a strapper in 2 way light switching, Ive marked it as C2 for two reasons, one being that there is no longer a cpc in the cable and also that the no live conductor has no proper insulation, however I couldnt find where on the EICR inspection schedule that it would go?

closest i could find on NAPIT EICR was condition of live parts?

Any help would be appriciated

cheers
 
Go on then Biff....hit me

i'll just get my trusty knuckleduster.

however , surprisingly , there is absolutely no requirement for a cable to contain a cpc just for the sake of protecting it , which is never guarrented anyway with t&e as you can nail through the live and not touch N or E.
but your on the right track with insulation - and lack of phase identification during the full run.
 
irrespective of what regs. it's breaking, it's a potential danger anyway , so a C2 is correct.
 
18241d1364928574-use-cpc-live-conductor-eicr-coding-2013-03-27-11.55.13.jpg
what! no sleeving, thats pretty shoddy. Damn beaten to it.
 

Reply to Use of cpc as a live conductor - EICR Coding in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I've tried to research and form a plan without asking on here, but I'm just going around in circles. Just completed an EICR. The wiring ranges...
Replies
15
Views
2K
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
798
I have been asked to look at this report as the customer has been given (in their words) 'A very high quote plus VAT'. It doesn't look well...
Replies
5
Views
598
Been to a fault finding job and lights where tripping the rcbo. After further investigation we found that it was a blue strapper cable (old...
Replies
17
Views
3K
Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock