Discuss Volt drop question in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Welcome to ElectriciansForums.net - The American Electrical Advice Forum
Head straight to the main forums to chat by click here:   American Electrical Advice Forum

O

oliver s

Hi all

Just had an enquiry for 50 kw ground mounted PV system, the proposed system is to be connected to a three phase supply In an industrial unit, the ground mounted array will be approx. 200mtrs away from the unit.
The inverters and generation meters are to be mounted next to the array.(standard meters will be in the unit)
Is the usual 4% volt drop acceptable for the ac supply or would it be calculated at 1%

Thanks in advance
 
It's a judgement call, I would say.

What is the grid voltage currently? If it is low then you can maybe afford to let the 1% rule slip. You do risk the possibility of problems in the future however if the grid voltage rises.

Unfortunately, as you have probably noticed, the cable size required to achieve a <1% VD are horrific at that sort of length.
 
Thanks Solar city ive not yet measured the voltage only initial enquiry but yes the cable size by a quick calc would be a 300mm!! at 1% and even at 4% a 95mm

Does that sound right?
 
Or run the DC back to the building and mount the inverters there, as I understand the voltage drop for high voltage DC is lower than AC and you will not then have the problems with the inverters shutting down because they have gone over voltage.

There must be a reason why the UK buys power from France in DC and we have an inverter station in Kent, Google it, it is an interesting read.
 

Reply to Volt drop question in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock