Discuss voltage between live and earth in the UK Electrical Forum area at ElectriciansForums.net

tommo1

-
Reaction score
2
hi all
im currently doing some testing on a university the install is metal trunking and metal conduit used as the earth for the whole installation. when we disconect neutral and carry out isulation resistance test we are getting a 12v between live and the earth bar, and our metrel tester wont allow us to carry out the test. does any one have any ideas.
thanks in advance
 
as spin says, induced volts. need to isolate other circuits while testing.
 
I would imagine, that your tester isn't allowing any tests, because the neutral has been disconnected, or you've altered the settings.
Should allow testing with voltage up to 50V, I believe.
 
long shot, but have you tried using an insulated screwdriver to press test? I had a metrel that would never carry out EFLI tests unless i did this, A symbol saying "phase voltage on PE terminal" came up and it beeped alot.
 

Reply to voltage between live and earth in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Old two core cable in a lighting circuit with no cpc at any point All points had metal fixtures and fittings class1 At two points the live loop...
Replies
0
Views
610
Hi all, New to the forum. I have been asked to look at this for one of our guys who's had an issue onsite after some electrical works had been...
Replies
4
Views
712
Hi was recently at a property and was installing a Solar PV system. was doing my testing and i came across a weird result when doing the...
Replies
23
Views
3K
Over the last few days, I have stumbled across a number of threads that seem to point to a prevalent misunderstanding. Either that, or I have been...
Replies
6
Views
2K
Hi All, I've installed a Lorex doorbell recently, but it is not turning on. I did some tests using a multimeter and this is what I found...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock