Discuss Voltage between Neutral and Earth in the UK Electrical Forum area at ElectriciansForums.net

Sb8389

-
Reaction score
25
Hi guys,
came across a fault yesterday on a job where I was getting 15v between neutral and Earth at two sockets on a ring main.if u need anymore details let me know.
i am unsure what would cause this and want your expert opinion as I have never come across this problem.

the installation is an old 3036 board no RCD
TNS system

your replies are appreciated
 
it could be a phantom voltage. try with an analogue meter. if it's still there, check all earthing and bonding and the cpc connections on the socket circuit.
 
Hi guys,
came across a fault yesterday on a job where I was getting 15v between neutral and Earth at two sockets on a ring main.if u need anymore details let me know.
i am unsure what would cause this and want your expert opinion as I have never come across this problem.

the installation is an old 3036 board no RCD
TNS system

your replies are appreciated

What was the voltage between neutral and earth, measured at the terminals in the board?
 

Reply to Voltage between Neutral and Earth in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi everyone, When checking my consumer unit voltages with the full board off, I stumbled across something head scratching. Measuring the feed...
Replies
1
Views
575
  • Question
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Replies
6
Views
405
Hello, I'm not an electrician, more one of those 'competent DIYers', so probably the worst kind :) My electric shower broke, the shower firm came...
Replies
13
Views
1K
Hi was recently at a property and was installing a Solar PV system. was doing my testing and i came across a weird result when doing the...
Replies
23
Views
3K
Hi all, Just a quick one, I want to use an ip rated light switch with a neon indicator to manually ovveride a PIR detector controlling an e27 LED...
Replies
1
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock