Hello all, just been thinking over Voltage drop!!

1. Where does the 3% and 5% figures for voltage drop (VD) come from? Appendix 4 (BS7671) gives the figures but why the different values between lights and sockets?

2. Also permitted voltage levels are -6% and +10% from 230V giving a min of 216V and max of 253V. If these permitted figures allow a voltage as low as 216V why can voltage drop only be 3% for lights (i.e bringing it down to 223.1V)?

Cheers..
 
The ESQCR percentage tolerances allow for the supply to reach your consumers terminals. You then have to ensure that the additional voltage drop in the installation is within limits.

Typically, lighting is more seriously affected by voltage drop. Fliament lamps especially, as the voltage falls not only does the light output decrease very rapidly but also the efficiency. So if you fit more / bigger lamps to counteract the loss of output, the consumption is increased. Compare electric heaters, where although the heat output reduces with the square of voltage, the efficiency remains constant, so under thermostatic control the element is just on for longer. Switched-mode power supplies will use the same amount of power regardless, as will some motors. And as mentioned above, discharge / fluo lighting is often one of the first things to fail altogether at the voltage falls, if it cannot strike.
 
3% lower than 216V, eventually discharge lights will drop out


Yep seen it on my road, neighbour has two MH Lights in garden (green and magenta), he rang me because they were failing, plugged MFT In and he only had 216. Knackered a tv and his fridge.

they fixed it, not sure how, maybe theres a big dial on the transformer!
 
Although bs7671 states 230v as the nominal single phase voltage for design calcs , no way does the dno use 230v as their baseline figure for distribution.
hence 9 times out of 10 the voltage at the terminals of a domestic cut-out is 240 or higher.

and the regs take into account that all of this is out of the installers / designers control and dont insist on a lower / tighter volt drop limit thats reliant on the dno voltage value , which could result is ridiculously oversized cables in trying to comply.
 
I think DNO transformers are still normally set up for 440/250V

This is why the argument about standardising the supply at 230v is wrong,to drop the voltage at the transformers would lead to an increase in the current across the network,which would cause major problems.In fact I don't think I have ever measured 230v at a house,they are usually around the 240v mark,I,ve actually had it as high as 253v in my house.
 

Reply to Voltage drop and it's effect? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Why is this still a thing, just done a quick calculation with the TLC volt drop calculator and if its a non lighting circuit the recommended size...
Replies
3
Views
910
So, the actual job is on a farm. I think I'll keep things simple at the moment and just ask about voltage drop. I'll come on to earthing and...
Replies
11
Views
2K
Hello, I live in Mexico, where I have a small, un-official trailer park on my property. The property is serviced by my privately owned, 650amp...
Replies
9
Views
1K
Hello, this is my first post here. I have a little experience with most types of household wiring through a decade of DIY remodeling, and...
Replies
0
Views
766
I'm getting a little confused about volt drop and 24v. I want to fit an LED strip light. 8m of lights 7w/m. It would be easier to have the 24v...
Replies
13
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock