Discuss Voltage Drop When Load Is Applied Question in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Reaction score
92
Hi,

I came across a situation recently while investigating a problem where measuring voltage at a set of 4 sockets read 243 Volts with no load, and when a 21 Amp load is applied, the voltage then reads 230 Volts.

Is it normal to have such a large voltage drop under load? Or does it imply the supply cable to these sockets is undersized?

Thank you.
 
Hi - over simplified it indicates the impedance of the supply is about 0.62Ohms, which is made up of the house wiring and the suppliers distribution network and overall your value is fine. By design we aim to keep below 7% V drop within the final outlet cct (say 16v) at designed load (say 32A). This V drop would be from your side of the meter to the socket (ie not including suppliers cable to your house) . Cheers, David.
 
Hi,

I came across a situation recently while investigating a problem where measuring voltage at a set of 4 sockets read 243 Volts with no load, and when a 21 Amp load is applied, the voltage then reads 230 Volts.

Is it normal to have such a large voltage drop under load? Or does it imply the supply cable to these sockets is undersized?

Thank you.

What was the voltage at the supply when the circuit was under load?
 
What was the voltage at the supply when the circuit was under load?

I did not measure the voltage at the supply, just at the load point.

I think I have been over thinking this. It is a 5% drop between the intake voltage source and the load point, not 5% drop between unloaded and loaded voltage. I was just wondering if from experience that big a volt drop is usual for 21 amps load or a sign of an undersized cable.
 
I did not measure the voltage at the supply, just at the load point.

I think I have been over thinking this. It is a 5% drop between the intake voltage source and the load point, not 5% drop between unloaded and loaded voltage. I was just wondering if from experience that big a volt drop is usual for 21 amps load or a sign of an undersized cable.
What size cable and what was the R1+R2?
 
Overall the volt drop is not too bad but it would tend to indicate that the socket circuit was wired in something like 1.5mm², but this is theoretical and any additional resistances from joints may cause this level of volt drop.
That said for a basic length socket circuit in 2.mm² unless it is on a 16A breaker (taking 21A!) the volt drop is too high for the circuit as it should be designed to be within limits.
A more likely scenario than being wired in small csa cable is that there is a high (ish) resistance joint somewhere that is causing the additional volt drop.
The above points about R1+R2 and the supply voltage are relevant to determining the cause, normal R1+R2 may mean a loose supply cable as demonstrated by a drop in the supply voltage.
If the supply voltage is stable then the likelihood is that the R1+R2 ( or rather the R1+Rn) is higher than it should be.
 

Reply to Voltage Drop When Load Is Applied Question in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi, I'm looking for a bit of advice on a volt drop query we have in our office. I'll explain the scenario and I would really appreciate any...
Replies
3
Views
594
I am sending power to some 5v led lights about 50ft from the transformer. I was going to use some CAT6 direct Burial cable that I kept after a...
Replies
2
Views
1K
Hello, I live in Mexico, where I have a small, un-official trailer park on my property. The property is serviced by my privately owned, 650amp...
Replies
9
Views
1K
Hello All and happy new year. Over the holiay I have changed all of my old sockets to some nice new ones and added a couple with usb sockets for...
Replies
4
Views
740
Hi senior members of the forum, I need advice on couple of questions about Rio and BHP specs for electrical installation purposes. What is the...
Replies
0
Views
794

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock