Discuss Voltage Optimisers is this going to save you ££££ what do you think in the Green Energy Forums | Green Energy Hub area at ElectriciansForums.net

W

Will Mcloughlin

I'v been looking into voltage optimisers

are you really going to save money
boasts savings on 8-10%

reducing incoming voltage basicly a step-down transformer
and prehaps reduces heat loss from over voltage

lower voltage higher current?
I I believe it's to reduce
IR from the Kvar KV calc
any thoughts?

many thanks

will
 
Anything electronic won't be affected at all as the power supplies will still use the same amount of power.
Heating elements will run at slightly reduced power but this will result in them taking longer to get up to temperature and so use the same, or possibly slightly more kWh.
Incandescent lamps will be slightly dimmer.

Generally speaking they don't achieve anything other than putting your money in the pockets of other people.
 
You would do better to think about what you do -tip one , don't fill the work vehicle with crap. It will cost you fuel and more wear and tear on the brakes and clutch etc.
 
You would do better to think about what you do -tip one , don't fill the work vehicle with crap. It will cost you fuel and more wear and tear on the brakes and clutch etc.
And as important if not more. Don't thrash the van at 80mph down the motorway.
Its basically a motorised brick and the lost fuel as you push it past 40-50 MPH really stacks up.
I know hourly rates are high but the 10 mins you save on a drive are blown in fuel and wear and tear.
 
@Pat H You are right.
Years ago we had major road works on a bypass . They imposed a 50mph speed limit on it backed up by speed cameras. This road was a major traffic hold up . When the work was finished they lifted the speed restriction , about a year later they reimposed it as the statistics showed the traffic kept flowing better during the restricted speed.
 
not only the fuel saving here. i generally cruise at a steady 60 on m ways and dual carriageways. gets me there a few minutes later, but more relaxed and less stressed out than if i'd been doing 80 and hitting the brakes all the time.
 
not only the fuel saving here. i generally cruise at a steady 60 on m ways and dual carriageways. gets me there a few minutes later, but more relaxed and less stressed out than if i'd been doing 80 and hitting the brakes all the time.

You are spot on. It is also the heavy braking that causes the tail backs in heavy traffic.
 
so basicly stay away

Iv actually fitted two of these
threw a wholesaler
just wounderd if they work

they did a survey and said they could sAve a hotel 10 -12 grand a year
off a 120 grand lecky bill
(big hotel)

surely that's a ballsy claim
the unit itself would be around
30-40grand
which got me looking at bespoke units
and the cost keeps going up

is it good sales tactics or are people / business saving money

Inductive loads i guess wont positively effect
but it must be down to electronics
capacitive loads
 
It is only resistive loads which will really draw less power when you lower the voltage, but they will have to be on for longer to do the same amount of work in the case of heaters or just be less bright in the case of lamps.
Electronics will generally draw more current at lower voltages to maintain the same amount of power.
Inductive loads like motors will do something that is beyond my knowledge but I'm pretty damned sure you'll end up putting more power in to the system to achieve the same amount of work.
 
All electrical loads require a certain amount of power to operate,
so if you adjust your voltage down, then the current rises to compensate
meaning the SAME amount of power is still used !
just in a different balance.
They are simply taking advantage of peoples technical ignorance.
 
A couple of years ago I was asked to do a review on one that was claimed to reduce energy consumption and this bills. It made my supply current look like this:

Correctedcurentwithmagicaldevice_zps35340807.jpg

And saved no energy.
 
First, I agree with all the remarks and arguments everyone has written so far. However, I have installed one in our home (a Vphase unit). Why?

My wife has a number of medical equipment which run permanently bu are actually only doing any medical function for much less of the time; I cannot put a figure on it but examples are her medical fridge which has a fan inside it which constantly circulates the air inside, an air bed which has a compressor running all the time even when the bed is made, various adapters for syringe pumps. There are also the usual number of mains powered equipment with a transformer inside eg: we have emergency lighting units and the TV/Video/Sky set-up in the lounge and in her medical room. The net load is a constant 250 odd Watts at 240Volts. With the Vphase regulating the house voltage to 220Volts this reduces to just over 200Watts.

The other reason I installed it is to address the way my wife and her carers use the tumble dryers (one for us and one for the dog's stuff). They don't use the automatic programmes preferring to use the timed mode. I cannot change this behaviour (but did try but the moaning and arguments were just not worth it so I adopted a technical solution instead using the Vphase). The consequence is that broadly speaking the dryers are operated in a time chunk of 30 minutes for the freshen/soften up after being on the line to dry or 60, 90, 120 minutes. These are the 'standard' times they associate with particular bundles of wet laundry. And they don't like having to having a second run to complete drying if they selected too short a dry originally so it means they tend to pick a longer than is actually necessary time period to dry in one cycle and be ready on completion for putting away in the cupboard. My Vphase unit actually then works in my interest by reducing the amount of wasted energy resulting from the way the dryers are actually used. I have not explained any of this to my wife or her carers and they have not changed the way they use the dryers. My electricity consumption has gone down.

I thought you might find the second paragraph an interesting angle on the effectiveness of voltage optimers.
 
First, I agree with all the remarks and arguments everyone has written so far. However, I have installed one in our home (a Vphase unit). Why?

My wife has a number of medical equipment which run permanently bu are actually only doing any medical function for much less of the time; I cannot put a figure on it but examples are her medical fridge which has a fan inside it which constantly circulates the air inside, an air bed which has a compressor running all the time even when the bed is made, various adapters for syringe pumps. There are also the usual number of mains powered equipment with a transformer inside eg: we have emergency lighting units and the TV/Video/Sky set-up in the lounge and in her medical room. The net load is a constant 250 odd Watts at 240Volts. With the Vphase regulating the house voltage to 220Volts this reduces to just over 200Watts.

The other reason I installed it is to address the way my wife and her carers use the tumble dryers (one for us and one for the dog's stuff). They don't use the automatic programmes preferring to use the timed mode. I cannot change this behaviour (but did try but the moaning and arguments were just not worth it so I adopted a technical solution instead using the Vphase). The consequence is that broadly speaking the dryers are operated in a time chunk of 30 minutes for the freshen/soften up after being on the line to dry or 60, 90, 120 minutes. These are the 'standard' times they associate with particular bundles of wet laundry. And they don't like having to having a second run to complete drying if they selected too short a dry originally so it means they tend to pick a longer than is actually necessary time period to dry in one cycle and be ready on completion for putting away in the cupboard. My Vphase unit actually then works in my interest by reducing the amount of wasted energy resulting from the way the dryers are actually used. I have not explained any of this to my wife or her carers and they have not changed the way they use the dryers. My electricity consumption has gone down.

I thought you might find the second paragraph an interesting angle on the effectiveness of voltage optimers.
You need a certaing amount of energy to dry the clothes. At whatever voltage. Don't get deceived.
 
I was considering installing one for my property so I looked into it.
Ive read the ombudsmans report on a trail made in a load of actual domestic households with voltage optimisers installed. The claims being made up to 10% saving are true.

BUT

Only in a very small portion of the properties.

The average saving was 4-5%.

Some made no savings at all or showed an increase.


It's a few months back so cannot remember exact figures, but it was an interesting read.


All the saving information I've seen on products are a saving between 8-10%

£500- £600ish to supply and install is a lot to spend if your one of the properties that save no money.

If your lucky enough to be the average 5% saving then you would save £25 a year on the average £500 yearly electric bill.

If your even more lucky and you save 10% that's only £50 per year.

I could go on and give you a saving on higher electric bills , but I won't . you do the maths.
 
I was considering installing one for my property so I looked into it.

If your lucky enough to be the average 5% saving then you would save £25 a year on the average £500 yearly electric bill.

If your even more lucky and you save 10% that's only £50 per year.

I could go on and give you a saving on higher electric bills , but I won't . you do the maths.

Why not pick one up from eBay and install it yourself? According to your payback figures, it'll pay for itself in 2-3 years:

VPhase VX1 VX1-2 Voltage Optimiser - Power Saving Voltage Optimisation! | eBay - http://www.ebay.co.uk/itm/VPhase-VX1-VX1-2-Voltage-Optimiser-Power-Saving-Voltage-Optimisation-/232341484983?hash=item3618a1b5b7:g:cLMAAOSwY3BZHtBG

I've got one at my house and, whilst it's difficult to quantify the savings (if any), it cost less than a tank of diesel and hasn't had any negative side-effects.
 
Why not pick one up from eBay and install it yourself? According to your payback figures, it'll pay for itself in 2-3 years:

According to the figures I've quoted if I am one of the few luck individuals who save £50 a year it will take 10 -12 years to pay off.

If I am not so lucky and make no savings it will never be paid off.

I'm not sure where you got your 2-3 years figure.

if I installed it myself I would save £200. I'm still looking at 6-8 years in the unlikely event i am one of the luck few.

In order for me to invest in a energy efficient money saving scheme I need to know I am definitely going to get my money back long term.

If the report came back and said everyone saves between 4-6% I would consider it.

Of course I could get a cheap China import knock off for £200 and fit that.
I wouldn't waste my time, as time is money.

It costs me £55 to fill my tank with diesel. I must have a small one, how big is yours?
 

Reply to Voltage Optimisers is this going to save you ££££ what do you think in the Green Energy Forums | Green Energy Hub area at ElectriciansForums.net

Similar Threads

Hello, I have a EV charger that is reporting over voltage and is unable to charge. the charger will operate up to 253V The solar inverter reports...
Replies
6
Views
3K
Hello, I live in Mexico, where I have a small, un-official trailer park on my property. The property is serviced by my privately owned, 650amp...
Replies
9
Views
1K
I own a top floor tenement flat that I used to live in and then rented out after I married. It is currently empty whilst some work is being done...
Replies
0
Views
140
I'm in the process of building a new house (West Indies). Due to terrain it is a modular design where each bedroom is an individual building...
Replies
4
Views
2K
So for the longest time I had issues in this location while gaming. I am on a second pc build that exhibits the same weirdness that made me...
Replies
28
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock