G

Graysonlad

I have been following a thread on another forum in which a guy reported that the neutral bar on a fused board was at times "glowing hot" At other times, when a neutral was disconnected there was a spark. This was on a 240 volt single phase AC supply. He also reported that when measuring voltage across neutral to earth he got a reading of 130 volts.
This intrigues as I have never come across this before. I have had three phase motors and three phase battery chargers burn out due to a phase having gone down on a three phase supply, but never this.
With regards to disconnecting the neutral, my own working rule is never disconnect a neutral whilst it is carrying current. I wonder if that could be the reason for the sparking i.e. it was in use?
Q 1: Would a bad connection on the earth or neutral be the cause of the 130 volts on neutral to earth?
Q 2: Testing across neutral to earth, on a sound/good installation, what voltage reading would you expect?
Q 3: Metering between Live and Earth what value would you expect?

Note: Having checked the single phase supply at my home I get approx 30 volts at:
Neutral -Earth. and the same again at Line - Earth.
Line to Neutral reads 240 Volts.
 
30v L to E tells me you not got an earth. N/E should be 0V. L/N - 230V
 
Last edited:
No earth and a L-E fault somewhere which is resulting in a voltage appearing on the earthing system relative to the neutral which is at 0v.
 
Last edited by a moderator:

Reply to Voltage reading between Line- Earth. Neutral-Earth 240 V AC in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top