Hi Guys
I would appreciate someone just casting their eyes over my calculations.
I carnt decided what to do I'm doing a kitchen renovation and existing 6mm 32a supply but I don't know whether to upgrade to 10mm and 40a breaker as the volex unit doesn't do a 45a
Diversity comes out at 22amps but I'm not sure what to do ?? Any advice as its a double oven and Hob total of 50amps
5100w double oven 22.17 amps
6400w Hob 27.83 amps
50amps total
Diversity
First 10 amps
Then 30% of the remainder so (40amps)
30x40= 1200
1200\ 100= 12 amps
10+12= 22 amps with diversity so a 32a 6mm supply is ok
My gut feeling is upgrade to 10mm and 40a breaker
What's people's thoughts ?
Cheers